Hi all
I have a 5 winding transformer and in the software I am working there is no possibility to model 5 winding transformer. Hence I need a work out such that I can replace the 5 winding transformer with 2 three winding transformers.
The name plate of the transformer is attached as a link. It is a start-Delta-Delta-Delta-Delta winding of ratings 10-2.5-2.5-2.5-2.5, 33/0.315kV/0.315kV/0.315kV/0.315kV winding .
Can anybody suggest me literature or some guidelines to model the transformer with three winding transformer.
Regards
I have a 5 winding transformer and in the software I am working there is no possibility to model 5 winding transformer. Hence I need a work out such that I can replace the 5 winding transformer with 2 three winding transformers.
The name plate of the transformer is attached as a link. It is a start-Delta-Delta-Delta-Delta winding of ratings 10-2.5-2.5-2.5-2.5, 33/0.315kV/0.315kV/0.315kV/0.315kV winding .
Can anybody suggest me literature or some guidelines to model the transformer with three winding transformer.
Regards






RE: Hi all I have a 5 winding transf
https://www.researchgate.net/publication/3574233_A...
RE: Hi all I have a 5 winding transf
RE: Hi all I have a 5 winding transf
Three winding transformer are more common. Perhaps we can suggest to use their modeling techniques as a reasonable approach to be extended to 5 winding units. Consider use 5-two windings transformer and define the mutual impedance between each winding.
Perhaps the links below could be used for reference:
1)hhttps://w3.usa.siemens.com/datapool/us/SmartGrid/d...
2) http://www.skm.com/applicationguides1.html
RE: Hi all I have a 5 winding transf
I was thinking of modelling the five winding transformer with two three winding transformer.
In my case the transformer is 10MVA , 33kV star and four nos of 2.5MVA Delta, 0.315kV in secondary. So I thought of replacing this 5 wining with 2 nos of five MVA so I can get
2 x(5MVA/2.5/2.5MVA) however that was not a good solution for me as It would require two input. Hence I thought of replacing with three nos of three winding transformers such that a three winding will feed two three winding hence I will have only one input and 4 output secondary. However I am not sure how I will split the impedances. As Five winding tx will have 10 impedances if required to accurately modelled.
I am not sure about how the vector group have to be considered.
Can I replace 10(Y)-2.5(d)-2.5(d)-2.5(d)-2.5(d), 33/0.315kV/0.315kV/0.315kV/0.315kV winding with 3 three winding TXs as follows such that
Tx1-10MVA/5MVA/5MVA (All star connected)
Tx-2- 5 MVA/2.5MVA/2.5MVA (Star- Delta -Delta)
Tx-3- 5 MVA/2.5MVA/2.5MVA (Star- Delta -Delta)
Tx1 will supply Tx-2 and Tx-3.
This way I get one HV and 4 LV delta connected however I am not sure how can I divide the impedances.
Any thoughts