Coordination of ground fault protection

Coordination of ground fault protection

Coordination of ground fault protection

(OP)
Hello everyone, we have utility supplied distribution transformer, having a three phase connection YY with both neutral grounded,
My question is
1. Does ground fault current magnitude in the secondary will be the same in primary, since the star point of two sides have common ground connection?
2. Does coordination of ground fault is possible?
3. Where to place the CT for 51N, at the primary or secondary side? or to have CT both in primary and secondary side.

Thank you in advance, for your unlimited sharing of expertise!

RE: Coordination of ground fault protection

1. Only if the transformer windings are of the same voltage, and the transformer has zero impedance.....No.
2. Likely the utility has any ground only protection set very high. Use the utility's phase protection as what you are coordination with.
Unless you know for sure there is a utility added ground device.
3. Use the secondary side for a ground CT.

The utility likely has many of these transformers, and buys them in bulk (unless it is very large to them) so the cost of replacing it is very low. So the utility likely has minimum in the way of protecting it. Use your own protection for your equipment.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources