×
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!
  • Students Click Here

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

Jobs

Sudden reduction of Power Factor in a Motor feeder

Sudden reduction of Power Factor in a Motor feeder

Sudden reduction of Power Factor in a Motor feeder

(OP)
In a 3 phase, particular motor feeder, the Power factor suddenly reduced from 0.98 to 0.82. The circuit is shown below,




The company is not sending me to the plant, anyway I would like to know the cause of the trouble for my experience. I'm thinking of blowing of capacitor fuse in one phases. If so, what would be the Kvar output from the capacitor bank from the 2 capacitor banks.It means the two capacitor banks are in series with applied voltage of 6kV. Also the operator observed the noise from the 6% series reactor. What could have possibly went wrong?

RE: Sudden reduction of Power Factor in a Motor feeder

No circuit shown charz.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Sudden reduction of Power Factor in a Motor feeder

The kvar output will be half of the full amount. Output is proportional to the voltage squared = V²/X. X = 2·pi·f·C.

Voltage across each phase before the fuse blows is VLL/sqrt(3). Voltage after the fuse blows is VLL/2.

Output of each phase before the fuse blows is [VLL/sqrt(3)]²/X = VLL²·2·pi·f·C/3. Total of all three is VLL²·pi·f·C·2.

After the fuse blows, the output of each phase is [VLL/2]²/X = VLL²·2·pi·f·C/4. Output of two phases is VLL²·pi·f·C.

RE: Sudden reduction of Power Factor in a Motor feeder

I can see it in the original Bill, must be you... poke

A blown fuse is a very likely suspect here. If I had to guess why, I'd say it was because of the primary reactor starting method and that the PFC caps are on line during starting. As PFC caps, the kVAR you select is for correcting the vars of the RUNNING motor. Starting current and the associated low PF causing stress to the PFC caps when started across-the-line (DOL) is not very significant because the duration is very short. When using a reduced voltage starting method, the amount of time the motor is pulling higher than normal current and lower than normal PF will result in the caps attempting to contribute more VARs into the circuit than they are rated to deliver for that extended time. They over heat and swell. You may not have actually blown the fuses if the caps have a "turkey timer" pop-out button indicating that their internal safety disconnect opened, but the effect is the same, the cap(s) is not available to the circuit.

On RV starting methods, I generally recommend having a PFC Cap Contactor ahead of the caps, isolating them until after the starting is done by controlling that cap contactor with, in your case, the reactor bypass contactor.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington

RE: Sudden reduction of Power Factor in a Motor feeder

Quote (jraef)

When using a reduced voltage starting method, the amount of time the motor is pulling higher than normal current and lower than normal PF will result in the caps attempting to contribute more VARs into the circuit than they are rated to deliver for that extended time.
How can capacitors attempt to contribute more vars into the circuit? Capacitors are passive devices that contribute according to the voltage impressed on them. Q=V²/Xc

RE: Sudden reduction of Power Factor in a Motor feeder

(OP)
I calculated the improved PF due to the capacitor bank after getting the motor details. The corrected PF comes to Unity (attached). With the Unity PF, there could be a possibility of resonance. I haven't done any resonance analysis up to now. How to do the resonance analysis? The details which need are Motor inductance, Capacitance of capacitor, and does the source impedance (from plant transformer till the motor terminal) matter?

RE: Sudden reduction of Power Factor in a Motor feeder

jghrist - I'm curious about that too.

RE: Sudden reduction of Power Factor in a Motor feeder

Maybe, the noise is coming from the motor, too? Having caps on just two of the phases would create negative sequence imbalance that might cause the motor to growl due to reverse torque.

RE: Sudden reduction of Power Factor in a Motor feeder

(OP)
If there is a negative sequence relay protection, can the feeder be able to detect this fault? If so, how should we calculate the percent of imbalance in case of single fuse blown in the capacitor?

RE: Sudden reduction of Power Factor in a Motor feeder

I see it now.
I remember a wise old head electrician. Whenever he passed a bank of caps he would lightly drag his hand across the cans. If one can was cooler he would have someone check the fuses.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Sudden reduction of Power Factor in a Motor feeder

(OP)
I was told that after replacing one of the capacitor, the power factor improved to 0.98. The fuse did not blow.
What could be the cause for reduced capacity of a capacitor?

RE: Sudden reduction of Power Factor in a Motor feeder

Quote (charz)

I was told that after replacing one of the capacitor, the power factor improved to 0.98. The fuse did not blow. What could be the cause for reduced capacity of a capacitor?
An open circuit in the capacitor (wire burnt open before blowing the fuse).

RE: Sudden reduction of Power Factor in a Motor feeder

(OP)
It was not a case of open circuit. When they ran the motor with 2 capacitors, the PF was 0.76, but when they ran with three capacitors, the PF was 0.82 and after replacing the faulted capacitor, the PF again increased to 0.98.

RE: Sudden reduction of Power Factor in a Motor feeder

Quote (charz)

It was not a case of open circuit. When they ran the motor with 2 capacitors, the PF was 0.76, but when they ran with three capacitors, the PF was 0.82 and after replacing the faulted capacitor, the PF again increased to 0.98.
Multiple cans per phase with one can open circuited?

RE: Sudden reduction of Power Factor in a Motor feeder

To expand on jghrist's post, internal fault, internal fuse. One of several sections.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Sudden reduction of Power Factor in a Motor feeder

It may be a capacitor that worn off, reducing it capacitance. This way, the reactance power will not be same, not correcting the power factor with the same efficiency

RE: Sudden reduction of Power Factor in a Motor feeder

(OP)

Quote (HamburgerHelper)

Maybe, the noise is coming from the motor, too? Having caps on just two of the phases would create negative sequence imbalance that might cause the motor to growl due to reverse torque.

Could you please elaborate? My understanding is that when the fuses of the capacitor bank blown, the Motor simply draws the required reactive vars from the utility on that particular phase. I understand that in case of the Main fuse on the way to motor terminal blowing, negative sequence current/voltage arises. But in this case,does the negative sequence currents or voltages exists because of blown fuse of the capacitor bank.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources