Hi Guys,
Recently our company structural engineers team have designed a high rise steel structure with special moment frames system+ special bracing frames which boosted by rotational friction dampers and used WUF-W connection for connecting beam to column. According to ACI-358-16 (PreQualified steel connections) ,section 2.3.2a Built-up Beams Members, The web and flanges shall be connected using CJP groove welds with a pair of reinforcing fillet welds (min 8mm) within a zone extending from beam end to a distance not less than one beam depth beyond the plastic hinge.
Also according to WUF-W criteria, beams should conform the requirements of Section 2.3., And according to Section 8, the plastic hinge location shall be taken to be at face of the column, So protected Zone is a distance equal depth of the beam at face of the column and in this zone, Welding flange and web of the beam should be CJP+ 8mm (Min) fillet weld in both side of the web.
Our Design was similar to above descriptions completely, Also WPS and Welding Maps of shop drawings prepared true But unfortunately steel manufacturer contractor did not observe these limitations and has connected web and flange just by a 8mm to 12mm fillet weld according to web thickness in both side, therefore there is not any sign of CJP welding.
Now one-fifth of structure has been constructed and erected and we are looking for any criteria for acceptance of as built connections or any other implement works like repairing or retrofitting the connections to satisfy prequalified connections code.
Your prompt answer will be appreciated.
Recently our company structural engineers team have designed a high rise steel structure with special moment frames system+ special bracing frames which boosted by rotational friction dampers and used WUF-W connection for connecting beam to column. According to ACI-358-16 (PreQualified steel connections) ,section 2.3.2a Built-up Beams Members, The web and flanges shall be connected using CJP groove welds with a pair of reinforcing fillet welds (min 8mm) within a zone extending from beam end to a distance not less than one beam depth beyond the plastic hinge.
Also according to WUF-W criteria, beams should conform the requirements of Section 2.3., And according to Section 8, the plastic hinge location shall be taken to be at face of the column, So protected Zone is a distance equal depth of the beam at face of the column and in this zone, Welding flange and web of the beam should be CJP+ 8mm (Min) fillet weld in both side of the web.
Our Design was similar to above descriptions completely, Also WPS and Welding Maps of shop drawings prepared true But unfortunately steel manufacturer contractor did not observe these limitations and has connected web and flange just by a 8mm to 12mm fillet weld according to web thickness in both side, therefore there is not any sign of CJP welding.
Now one-fifth of structure has been constructed and erected and we are looking for any criteria for acceptance of as built connections or any other implement works like repairing or retrofitting the connections to satisfy prequalified connections code.
Your prompt answer will be appreciated.






RE: WUF-W Connection
If you have space, one option may be to bolt on flange plates or the Kaiser bolted bracket.
RE: WUF-W Connection
Yes, All shop drawings have been submitted and signed by all stakeholders, also they have accepted their's fault but it is not solution, the main question is, what is the best solution?!
If we add bolts on flanges or any thing like that, we can not change the criteria that we need CJP groove weld in protected zone, in all connections we need cjp because of plastic hinge and high degree of rotation in this zone and high level of fracture in this location
So what we have to do?!
RE: WUF-W Connection
With that said, can you revise to a different prequalified connection? I had suggested the Kaiser bolted bracket. I believe that does not require welding. We've used it in the past to retrofit pre Northridge moment frames. Any potential for this?
RE: WUF-W Connection
RE: WUF-W Connection
About CJP, comment of sandman21 is true completely,Connection Type will specify length of protected zone at face of column and in this zone we have to connect flange and web by CJP groove weld. Also in AISC 358 in built up section has been stated built up members should be similar to rolled section and i think it want to achieve a uniform section to see a uniform plastic deflections with minimum deficiencies and fractures. Therefore it seems the CJP is mandatory!
About Kaiser Connection in AISC 358 section 9.3.1 has mentioned Beams shall be rolled wide-flange or built-up I-shaped members conforming to the requirements of Section 2.3., then this type of connection needs CJP welds too.
Finally the only way is testing,is not?
RE: WUF-W Connection
any thing like repairing or retrofitting ?
assume this building had built some years ago and web and flange of built up beams connected by fillet welds, there is not any way to retrofit them according to FEMA ?
RE: WUF-W Connection
In my opinion, the main lesson that the structural engineering community learned from Northridge is that structural engineers aren't great at predicting cyclic connection ductility. That's why decided to stick to systems that have been previously verified by testing (prequalified). Out of pragmatism, we do set the bar a bit lower for retrofits. It's a slippery slope to start classifying the correction of new build mistakes as retrofits however.
Is there any way to modify your system so that less ductility is required and some of the mure onerous requirements would no longer apply?
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
RE: WUF-W Connection
You don’t show any element sizes or thicknesses, nor do you spell out the beam depth (protected zone length). You do say 8 or 12mm fillets, each side, as a function of the web thickness; pretty typical built-up beam fab., actually/normally a function of the shear flow. It would be helpful if you showed a couple sketches of these beam connections with all dimensions and weld sizes, etc. The reason for the CJP weld, flange to web, in that region is the extreme energy absorption actively going on in that region during hinge formation and reversal, and the want/desire to be more sure that there is no unprotected weld roots, with lack of fusion, crack starters, etc., during that high stress activity. Could you back gouge, from one side only, through the fillet and web and into sound metal at the root of the other fillet, providing a new groove to be rewelded for length “d” (beam depth, plus) out into the beam. Half of these welds would be down hand and half over head, but from only one side. I would probably preheat (post heat?) the connection to slightly soften or relax the region re: residual welding stresses, etc. And, I would not over match (by much) the base metals with my weld filler metals and process, so as to allow as much ductility as possible. I’d sure want the advice of a good welding engineer/metallurgist in setting up my weld procedure, process, etc. Then, I’d probably take him with me to meet with the AHJ for their approval.
RE: WUF-W Connection
RE: WUF-W Connection
RE: WUF-W Connection
Note: The OP is asking about welds for the built-up beams. I don't think he is asking about the beam to column connection welds.
RE: WUF-W Connection
Thanks a lot for your help on this issue, thanks to all
At first i want to explain just a little more about our project.
Our Structural system is special moment frames in two directions and general arrangement of frames is Tube in Tube system with a rigid core in middle.
In external tube , Columns are closely together and we have a column in each 3 meters, so the depth of beams will be limited about one-seventh of clear span of that, Assume that Longitudinal dimension of column is 600mm, So clear span of beam will be 300-60=240mm and total depth of girder will be limited to 240/7 ( Approximately 350 mm).
We have wide range of spans and wide range of girder depth too. they have been summarized in following tables :
Also Following detail is general type for our connections and beam splices.
RE: WUF-W Connection
1- The contractor could remove and replace the non-complying members. I recognize that this would be very costly and possibly dangerous. However, this solution would bring you into compliance
2- The contractor could burn off the existing welds, properly prepare the webs for CJP welds, and then complete the CJP weld. I recognize that this would be very costly and possibly dangerous. However, this solution would bring you into compliance
3- Connections in IMF and SMF must be either prequalified or qualified by testing. Requirements are provided in Chapter K of the AISC Seismic Provisions. Though not exactly what was intended, you might choose to “post-qualify” the connections that exist in the structure. This would involve building test subassemblages reflecting the actual conditions and then testing them per Chapter K of the Seismic Provisions. If the tests are successful then the conditions can be left as they are. If not then they will have to be repaired. This option might be a good one for gamblers. The tests will not be cheap (over a decade ago I got an estimate of three tests required per configuration at about $50,000 per test). If the tests work the testing may be cheaper than the repairs. However if they do not work you will have the cost of the tests and the repairs
So it seems there is not any simple way !
RE: WUF-W Connection
I've been thinking about how one might reinforce this if one were in fact alllowed to reinforce it. You know, first principles. And that got me to wondering: why are these demand critical welds?
At first, I thought that the answer would be obvious. You have to develop the plastic moment so you have to develop reliable horizontal shear transfer to go along with that. But that's not actually true. On the column side of the hinge, 100% of the required horizontal shear capacity is provided by the column panel zone. So there's no problem there.
With respect to important jobs that the welds are doing, all I can come up with is that they prevent the compression flange and web plate edge from buckling. And one would think that would be a relatively easy thing to reinforce for. But, then again, there is that clever engineer hubris problem that I mentioned earlier...
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
RE: WUF-W Connection
Not so. My sketch and analysis specifically detailed forces associated with plasticity and the web and flange buckling that might occur under cyclic dynamic loading. One can only get so "dynamic" in a quick, 2D, stationary sketch. I get that testing is required for complete understanding and alluded to it twice above myself. I'm trying to dive a little deeper.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
So the welding in this location is not according to capacities.
Therefore if beam fails before complete rotations beacuse of weakness in protected zone, ductility of system will reduce and whole of frames will collapse.
RE: WUF-W Connection
No worries, I'm with you on this. Everything in my previous responses assumed and implied cyclic, inelastic behavior.
Firstly, with the right reinforcement scheme, I suspect that you could create a section capable of achieving full plastic section moment over 0.04 radians. That's pretty much what I've been getting at.
Secondly, while I agree that it's necessary to achieve the 0.04 radians, I'm not sure that it's really necessary to achieve the full section plastic moment. All that matters is hitting that level of rotational ductility while maintaining a substantial measure of load resistance. Were the web flexural capacity to be considered sacrificial, you might get some degree of strain softening which is always undesirable. I would argue that the impact would be small and that normal strain hardening would kick in after an initial dip however.
It's important to remember that, in these systems, we're primarily designing for a particular amount of rotational/displacement capacity, not a particular level of load resistance. Consequently, there really is no required load capacity for the welds in this situation other than that expected to arise as a result of rotation. The litmus test for successful performance is simply whether or not the welds remain in tact up to the 0.04 radian displacement so that the web and flanges continue to stabilize one another locally. At least that's my take on it.
If you stabilized the flanges to prevent local buckling, I would argue that you likely would still achieve complete rotation capacity. You might even be able to achieve that rotation at a lower Mp as a result of the web not participating fully which would serve to increase the safety margins on the member of your system designed for capacity/over strength.
With this situation, I feel that the following is likely true:
1) You won't be able to negotiate any further with the AISC 358 committee. You'll simply have to do as they've instructed already. As such, I wouldn't waste too much time trying to argue your way into a lower cost solution.
2) My, very strong, gut feel is that you've got a great system here and that the code deficient welding really does not compromise that. Another thing that you've got going for you here is that the entire perimeter of your building is moment frame rather than just having a few isolated moment frames. And you've got the rigid core. That means a lot of redundancy so, if a handful of welds did give way AND that materially affected the performance in a few of those failures, would that really be such a big deal? I would argue not.
3) The cost of the remedy, per the AISC 358 committee, will be enormous. As the engineer of record, I would consider it my duty to the client, and society at large, to at least make a modest attempt at selling the AHJ on a non-tested reinforcement fix. That, even acknowledging that your odds of success would be extremely low.
4) The only way that you'll have a fighting change of being successful with #3 is if you're able to tell a good story about why the system is fine as is. A story that speaks to the fundamentals of the behavior that the code provisions are intended to encourage. I'm trying to help you come up with that good story.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
RE: WUF-W Connection
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
RE: WUF-W Connection
Not at all, assuming that you're addressing my proposals here. I'm talking about a system where the vertical shear resistance remains as it started: as passing through a web welded to the column flange. That ameliorates the differential vertical stiffness issues associated with bolted web connections.
I don't know the contractural arrangements of the project. There are arrangements under which the owner may well share in the cost and schedule savings associated with avoiding a needless repair. Regardless, at the end of the day, all resources are society's resources and they should be deployed efficiently.
Even if it's the correct story? You seem to imply that I'm being cavalier about the whole thing. I'm not. I'm attempting to be creative, flexible, and technically responsible. Everybody makes mistakes. And that includes engineers as well as contractors and fabricators. As much as possible, my preferebnce is to work with folks creatively and collaboratively to correct miststakes rather than to just beat them over the head with inflexible regulations. High seismic design, of course, has gone the other way out a combination of real and perceived necessity.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
What part of your story is correct? You cant answer the fundamental questions regarding behavior or forces in the beam web during a seismic event or even testing. You would have to begin at that point to try and convince anyone that your creative approach satisfies the intent of the requirements. Your assumption regarding failures in perimeter moment frames not being a big deal, without knowing the configuration or performance criteria of building is also unconvincing to try and tell the story that the welds are satisfactory. Its not a matter of being cavalier its matter that your story lacks fundamentals.
RE: WUF-W Connection
Not sure how easy it would be to quantify the force required at this joint since the weld strains will need to be compatible with the distortions caused by local flange buckling that will occur after multiple cycles. Testing has shown that nominally sized fillet welds at this joint have proven to be the weak link (Link). The AISC 358 commentary mentions that most of the testing done on built-up beams used end-plate moment connections, and if we look at section 6.4 we see that the requirement for CJP welds is relaxed to fillet welds sized at 75% of the web thickness. I suspect that as long as the welds are sized to develop the tensile strength of the web (75% thickness), there is a strong chance that the system will behave as intended.
Rantamental...Testing will be required, no doubt about that. But I think you would put the odds of success in your favor if you tested a configuration that used fillet welds sized at 75% of the web thickness. The contractor would need to repair the welds that don't currently meet that, but that would be a lot less work than repairing with CJP welds. I would also make the welds demand critical given that yielding is expected in this region, although this is not required by AISC 341 as far as I can tell.
RE: WUF-W Connection
I'd agree if my proposed shear resistance mechanism were soft or brittle. It's neither.
Possibly all of it. Definitely the significant observation that there is a limited demand for the web to flange welds to serve as horizontal shear transfer.
As I see it, I've been been meticulously answering all of these questions. What exactly is it that you believe that I've missed?
OP said that this was a perimeter tube moment frame system with tight column spacings (Fazlur Khan variety). I took him at his word, particularly after he posted details that would seem to confirm the assumption. The permiteter tube moment frame system embodies a lot of redundancy as I mentioned. It's an internet forum for Pete's sake. If we all hung back waiting for complete information, nothing would ever get done.
I disagree. If anything, I believe that I've been doing more than my share to chase down the fundamentals. Heck, I'm the only participant other than the OP to post a sketch. Most of what's materialized here seems to be just "follow the code" and the usual seismic catch phrases about ductility etc. I understood that OP wanted some out of the box problem solving and that's what I've been attempting.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
Probably not too easy. My intention was to try to hone in on just what we need the welds for and then, using that information, try to generate an intelligent reinforcement scheme. Similar to your recommendation regarding the 75% welds, one might just default to trying to replicate the original capacity/rstraint condition.
With reinforcement in play to address other issues, my biggest concern with my previous proposal would be the need for the potentially disconnected web to resist the moment implied by the eccentricity of shear delivery at the hinge (red stuff below). There's no doubt that the omission of the penetration weld make things less good. The more interesting question, in my opinion, is whether or not that makes things less than good enough. It's tough to say without testing of course.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
Based on the research in the link I posted above, we know that nominally sized fillet welds are not good enough. For the built-up sections that were tested, the failures initiated with yielding, followed by flange local buckling, followed by flange-to-web weld rupture. It's clear that the distortional forces caused by flange buckling place excessive demands on the welds. Since these forces are next to impossible to quantify, the prudent course of action is to size the welds to develop the web. Although I appreciate your effort to think outside of the box, the analysis in your sketch could never have predicted that type of failure. In this case the decision to develop the web is not the default choice for the sake of conservatism, it's a carefully considered choice given all of the information available.
In my mind this is similar to the new requirement in AISC 341-16 to size gusset plate welds to develop the strength of the plate for SCBF systems detailed to buckle out-of-plane. Testing showed that weld tearing was caused by out-of-plane rotation demands on the gussets due to brace buckling. That never would have been captured by traditional analysis.
RE: WUF-W Connection
1) Any chance you'd want to reference some specific pages or sections to save me a bit of review time? I wan't to benefit from what you've shared but the document is 250 pages.
2) I mispoke. Please consider my previous comment revised as follows:
Strategic reinforcing being something less onerous that gouging and full CJP of course.
But I did predict that type of failure in my sketch as being the critical issue. That's what the squiggly line and the reference to buckling were about. And based on the research that you provided, it kinda sounds as though I might have been on the mark. So perhaps engineering judgement is still worth a little something after all.
I don't see why it should be impossible. We do very much the same thing when providing restraint to rebar in the plastic hinge zones of shear walls etc. And again, a fall back position could be to reinstate the tensile capacity of the web by some means other than CJP welding.
I think that it's worth noting that we're all in agreement about most everything here. Very early on in this thread, I myself stated that 358 compliance would almost certainly be required. And I elaborated on why I thought that justified. I also brought up many of the same issues related to cyclic, inelastic behavior that are now being used to critique my own ideas. All I'm doing here is extending the conversation in an attempt to further understanding and creative problem solving.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
This is only statement you've made that I take exception with. The testing has shown nominally sized welds to be deficient. I don't believe it is possible to prove otherwise without additional testing.
RE: WUF-W Connection
For interest's sake, imagine a hypothetical alternate universe in which Northridge had not happened and we were still at liberty to merrily apply our own, hubris laden engineering judgements. How would you go about specifying a reinforcement fix? I've shown a proposal of my own below for review. Some things that I was hoping to accomplish:
1) Prevent flanges from pulling away from webs.
2) Prevent reinforcement itself from increasing the plastic hinge yield moment.
3) Avoid unacceptable stress risers.
The one weakness that concerns me is that I worry that the pretension in the bolts might mess with the welds if the flanges to not bear tightly against the web.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
RE: WUF-W Connection
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
RE: WUF-W Connection
1) The particular girder detail shown has 30mm thick flanges, which are slightly thicker than the 1" limitation in AISC-358. Also, the clear span-to-depth ratio (2400mm/350mm = 6.86) appears to be slightly lower than the minimum ratio of 7 allowed for SMF. In practice, are these slightly out-of-spec values acceptable for prequalification?
2) NERHP Tech. Brief No. 2 seems to discourage the use of deeper column sections: "deep wide flange
sections, particularly those with lighter weights, are susceptible to undesirable local and lateral-torsional
buckling. The performance of deep column sections is the subject of ongoing research". Wouldn't the skewed connection in this design exacerbate the likelihood of LTB? Can LTB be confidently resisted by lateral column bracing or is that one of the issues that future research will address? Is there any allowance for prequalified connections to be slightly skewed?
RE: WUF-W Connection
As people have mentioned your first sketch is not a accurate approach when considering a moment frames behavior at .04rads. Large strains and forces develop in the interaction between the flange and web, which also increases the forces in the flanges. You are not the first to suggest beefing up the fillet welds as a means of retrofitting but that testing would be needed to determine the adequacy of the connection and the effects of the HAZ on the flange. A system which removes part of the web connection to the flanges exists SSDA, it still requires compliance with Section 2.3. Your new fix would have a large impact on the capacity of the flanges, likely causing a rupture to occur at the long slotted holes.
RE: WUF-W Connection
I didn't suggest beefing up the weld. Perhaps you were addressing Deker there. I did find the parallels with the 75% provision in the bolted end plate section to be one of the more salient arguments presented here however.
Facinating. Thanks for sharing that. Sans pre-qualification testing, if basically is what I sketched out conceptually.
There already exists a pre-qualified bolted flange moment connection. Seems to me that the bolt holes should be resolvable.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
I agree. I can't answer all of your questions but I'll chime in where I've got something to offer.
I would think so. Firstly, your beam axis no longer runs through the column centroid. Secondly, there would be a component about the plastic hinge moment that would now induce weak axis bending in the column.
You'll generally have two kinds of column bracing at each floor level:
1) Translational perpendicular to the frame as provided by infill beams etc.
2) Torsional provided by the weak axis bending of the frame beams and any supplementary bracing. Hopefully the frame beams are still capable of adequate torsional support once they go plastic. It's not a problem that's arisen in testing to my knowledge. It's an issue that would probably also benefit from the hinging not taking place right at the column flange face.
Between floors, the columns are usually unbraced of course unless you've got girts etc in play. That's fine so long as design assumptions reflect reality.
Since this got through plan check, presumably there is such an allowance. Perhaps OP can elaborate.
I was flipping through 358-16 last night to check out some of Deker's references. One thing that I noticed was that they've extended pre-qualification to some of the more exotic column shapes. Built up box columns, cruciform I-shapes, etc. Interestingly, the decision to include these shapes was based on judgment rather than testing. To paraphrase the reasoning:
Meh. So long as the inelastic hinging happens in the the beams, may the columns aren't such a big deal after all.
So I guess there's still engineering judgement at work on the west coast after all. It's just concentrated in the hands of the hyper-qualified/pre-qualified.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
You did suggest talking to the AHJ and trying to get a non-tested reinforcement accepted. One would assume you were talking about reinforcing of the welds. Regardless it has been suggested before to test larger fillet welds as a means to resolve the issue.
Your concept relieves no stress from the flanges and the slotted web still has the same CJP requirements other assemblies have. It would be a stretch to apply the basic concepts.
Are we in your hypothetical world or the current one? Does your hypothetical world have any pre-qualified? You cant go jumping from world to world without laying down some ground rules.
RE: WUF-W Connection
Fair enough. The ground rules of KootK Hypo-World are these:
1) No regulations impede the free use of engineering judgment in any way.
2) All information from all worlds, past or present, is available to inform judgment.
In this way, one could know of 358 and the research that underpins it without being bound to follow its requirements.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: WUF-W Connection
Thanks to all for your nice comments and beneficial negotiations
I have to say that we are consultant of this project and it is not possible for us to give or not a permission according to engineering judgment or theoretical sketch or traditional analysis! Any document should has a strong international reference and could be defend-able in any Court that may be formed in near future. I know, maybe (In real world maybe) that current fillet welds pass criteria of codes, but could you sign the permission documents and acceptance of current fillet welds with confidence with out any extra test? Also accept complete responsibility for this permission and defend it legally with out any testing ? Something about 1700 Tons of structure has been manufactured and erected with this deficit.
Yes, you are true but our documents for designing has a supplement that allow us to use built up beam with flange thickness up to 30mm instead of 25mm.
Also span to depth ratio is 6.66 in critical girder and ratio of allowable value to current one is (7/6.66=) 1.05 and we were allowed to going beyond up to this. (5 Percent in all sections)
Be careful that there are a lot of issues which mentioned in AISC358 sections and commentaries that are not clear in theoretical( Limitations: Unit weight of girders, height of beams, span to depth ratio, beam flange dimensions, value of Cpr and Etc) and adopted from a lot of tests. Now, Could we get a unique result from all discussions or not?
RE: WUF-W Connection
We can NOT...
You get to pick what you can live with, prove to your satisfaction, and defend, we can’t/won’t do that for you. You certainly have been given a bunch of good, reasonably well thought out ideas and opinions, now it’s your job to apply your engineering judgement and experience to resolve the problem. You will have to be something of a diplomat to bring all the parties together, particularly the AHJ, and you hope they will be willing cooperative and constructive participants. When the fabricator, erector and GC consider the other possible alternatives, they should be able to find some money for testing, or whatever else is needed, to come to a reasonably acceptable resolution of this nasty situation.
RE: WUF-W Connection
I am with you and agree you
For us the most important issue is structure, safety and performance, so we offered just two following options
1- Test according to AISC 358 chapter k
2- change the members that do not comply criteria or change welds
It is clear that we can not accept any thing with out test, it is rule of engineering, try and error to find the way
Both of them are costly undoubtedly, but we could not find any better way, also I think the second one is impossible!!
Thanks to all for your helps and comments
RE: WUF-W Connection
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.