SELV 24VDC Power Supply - Measuring 90V AC!
Hi Everyone,
I have been arguing with a supplier of mine about a 24V DC power supply which is supposedly SELV compliant to EN 60950. When doing my usual testing of SELV supplies I measure the voltage across any two conductors on the DC side to ensure they do not exceed ELV levels (as one should expect from an SELV supply). The +ve to -ve terminals I measured as 24VDC no problem, but when I measured from either +ve or -ve to earth I got 90V AC with 50Hz ripple!
Am I going mad, or does this not comply with the requirements of SELV?
The power supply in question is a Carlo Gavazzi SPM1-241 (datasheet)
I believe this 90V AC is due to the capacitive coupling through the transformer as it is not screened and there is no earth terminal on the power supply itself. They are only relying on double insulation, but this doesn't stop the capacitance.
My supplier is arguing that this is OK as when you test to the SELV clauses in EN 60950 you only test for AC or DC depending on the supply type. They reckon that if the power supply is DC, you only need to test DC voltages. If the supply is AC you only need to test AC voltages.
I completely disagree as by this argument you can have a full exposure to 240V AC on the ELV side so long as the power supply is DC.
Does this not scream potential for electric shock to anyone else and complete void the purpose of SELV in the first place??
RE: SELV 24VDC Power Supply - Measuring 90V AC!
Whether such arrangements are acceptable in terms of compliance with 60950, I've got no idea.
EDMS Australia
I haven't got the copy of the standard it in front of me right now, but I don't recall seeing anything in there as far as allowing capacitive potential. I figured it was pretty cut and dry when it said (paraphrasing):
It pretty much says the same thing in AS/NZS 3000 for SELV..
For what its worth, I just went and checked a bunch of double insulated power supply devices here, and most of them indicated around 100V output to earth too, with my trusty high impedance Fluke. If I had an analogue meter I'd go check it again, but I don't.
I agree though, the argument that only AC or DC is measured is spurious and doesn't inspire confidence.
This document, whilst not dealing with the same sort of equipment, tends to state the same thing, its a potential that only shows up with a really high impedance measurement device, rather than being any sort of safety issue.
EDMS Australia
Now that you mention it, I do recall something in 60950 about using a 5kOhm resistor across the voltage measuring instrument for measuring between a conductor and earth. I should give this a try, do you think this would still be valid with my highZ DMM?
This could be the way out, though not the way my supplier is thinking. If I measure ELV with this resistor in place then it should be compliant according to the standard.
I'll report back...
In this situation, the immediate instinctive reactive should be to consider if there's supposed to be a load of some sort applied.
edit: I also recall one similar case where, after I'd made sure it was safe to do so, I switched to measuring the AC *current* leakage to ground. Obviously one doesn't just switch the meter to AC Current and measure. One must first make sure that the current is just uA leakage and that it's safe to ground that terminal via the current meter.
In your case, that current or charge needs to be miniscule to protect electronics from getting zapped. A problem often can occur if one circuit is connected to another where the two are on different AC systems. Most of the time, little or no harm occurs, but if one AC circuit gets discharged through the other, the circuitry that carries this discharge current could get damaged, either outright or latently. The latter would be a big problem for a production environment, if the outgoing product is weakened by this configuration. In this case, imagine that your circuit is connected to this power supply and you probe the circuit with a properly grounded oscilloscope. That 90 Vac difference could be discharged through and internal node with the board and partially damage the internal circuitry,
TTFN (ta ta for now)
I've been reading up on highZ measuring equipment and why it's bad for what I'm trying to do.
I've tested the PSU again this time with a 10k pot between +ve and earth and varied the resistance. Straight away the voltage dropped to less than 2V and kept dropping down to the mV range when I reduced the resistance.
I also went back into EN 60950 to find the clause about the resistance:
I'm satisfied now that this PSU is SELV compliant (and now I need to go test some of the other supplies I knocked back!)