AC Panel Connector/Conductor Question
AC Panel Connector/Conductor Question
(OP)
Hello everyone, I would love some insight on something...
2x 4/0 cables are going to a panel's main lugs but the maximum size of the panel's main lugs look to be 250kCMIL. Just wondering what's the best way to do this if at all?
Do you crimp them into a pin like connector? or is there like a splitter for this type of situations?
As always, i look forward to your input! Thanks.
2x 4/0 cables are going to a panel's main lugs but the maximum size of the panel's main lugs look to be 250kCMIL. Just wondering what's the best way to do this if at all?
Do you crimp them into a pin like connector? or is there like a splitter for this type of situations?
As always, i look forward to your input! Thanks.






RE: AC Panel Connector/Conductor Question
A 250 MCM lug will probably be rated for a 4/0 cable. Don't put two cables into one barrel of a lug. If these are single barrelled lugs, then consider changing the lugs to double barrelled lugs.
Bill
--------------------
"Why not the best?"
Jimmy Carter