Surcharge Caused by Railway Spur

Surcharge Caused by Railway Spur

Surcharge Caused by Railway Spur

(OP)
I am checking a sheet pile bulkhead along a river, with a railway spur in the active zone. Does anyone have a reference for the surcharge (PSF) to use for analysis?

DaveAtkins

RE: Surcharge Caused by Railway Spur

Dave:
Can you find out what the rail traffic is to get a handle on the intended loading? Can treat as a line load. Do you have access to a good geotekkie?

Dik

RE: Surcharge Caused by Railway Spur

(OP)
Yes, we have geotechnical engineers in house. I will check with them.

DaveAtkins

RE: Surcharge Caused by Railway Spur

I think that AREMA (American Railway Engineering & Maintenance) has a design document that has loading information in it. (not a 100% sure of this but it's worth exploring)

https://www.arema.org/publications/mre/index.aspx


RE: Surcharge Caused by Railway Spur

(OP)
My geotech recommended using a 2000 PSF strip load, for the width of the railway ties.

DaveAtkins

RE: Surcharge Caused by Railway Spur

Most railroads require a Cooper E80 surcharge which is an 8.5' wide strip load with a vertical pressure of 1,882 psf (= 80,000# axle load at 5' spacing on 8.5' wide ties). Sometimes, a railroad will also specify a percent increase for impact. In addition, most railroads require this load to be applied using Boussinesq analysis for a rigid wall. Most railroads I deal with have specifications on application of this LL surcharge. Check AREMA.

www.PeirceEngineering.com

RE: Surcharge Caused by Railway Spur

Thanks PEInc...

Dik

RE: Surcharge Caused by Railway Spur

DaveAtkins:
I’d check with the servicing RR and/or the RR which owns the spur, they will tell you what they want you to use, they try to keep pretty tight control over this kinda stuff. They really hate picking engines out of the water. They all have their own pet criteria for these things, although it will likely be in the range of what Peinc laid out.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources