Design purlin with seismic forces by asce7:2010

Design purlin with seismic forces by asce7:2010

Design purlin with seismic forces by asce7:2010

(OP)
How can i design girts and purlin (roof member) with seismic forces by asce7:2010? Can i utilise item 13.3.1 "seismic demands on nonstrucutral components / seismic design force"? How can i classify "ap" (table 13.5-1 or 13.6-1) and "Ip" (section 13.1.3)?

RE: Design purlin with seismic forces by asce7:2010

Unless they are part of your lateral force resisting system, they are usually not designed for seismic forces. The exception would be if they support some type of equipment, unique feature, or other architectural component.

RE: Design purlin with seismic forces by asce7:2010

(OP)
Hi MotoroCity,

This members (girts and purlin) aren't part for the lateral resisting system. They are only for suport roof deck.

RE: Design purlin with seismic forces by asce7:2010

The roof deck has a mass and theoretically would contribute to the seismic force but it would be EXTREMELY small. Unless you had cladding with significant weight, like a precast wall, the seismic force would be negligible. In such a case, you would simply select the appropriate ap value from the table and design the member accordingly

RE: Design purlin with seismic forces by asce7:2010

It may be that the girts are designed for all the typical D+L, D+S, etc. load combinations but also combos with the Ev (vertical seismic) component).

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Design purlin with seismic forces by asce7:2010

(OP)
JAE, in your opnion, we need design girts and purlin with seismic effects?

RE: Design purlin with seismic forces by asce7:2010

I think they're indicating you at least need to determine if the seismic load combination could govern when compared to the other load combinations seen by the purlin. Most often the seismic loads seen by purlins do not govern their design.

RE: Design purlin with seismic forces by asce7:2010

For the vertical force use ±0.2SDSWp per 13..3.1. Usually the diaphragm resists the horizontal component. If not, I would assume it is similar to an exterior wall in table 13.5-1. The importance factor, Ip, is typically 1.0 except risk category in IV buildings where it is 1.5. As the other have said, the load combinations with snow or full roof live load typically govern.

RE: Design purlin with seismic forces by asce7:2010

(OP)
wannabeSE, thanks a lot.

In your opinion, we can design by (asce7:2010 - 13.3.1):
Purlin: vertical force = ±0.2·SDS·Wp (usually the diaphragm resist the horizontal components)
Girts: horizontal force = Fp = 0.4·ap·SDS·Wp/(Rp/Ip) · (1+2·z/h)
?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources