equivalent THDv

equivalent THDv

equivalent THDv

(OP)
Hi,
I have 2 transformers on which I could measure THDv on the LV side. 1% on 1st transformer (2.5MVA), 2.1% on the second one (2MVA).
Both Transformers are supplied by the same 13.2kV switchgear
Is there an easy way to calculate the equivalent THDv on the 13.2kV side?

Thanks

RE: equivalent THDv

No.

I assume that those two transformers have nothing more in common than the primary voltage. And that they are loaded. The load is what determines THDV to a great extent, probably around half of the THDV contribution is from the load. The only thing you can say for sure is that the 13.2 kV THDV is less than 1%

Aren't there any PT:s on the 13.2 kV side? It is an easy matter to measure there. My guess is that you wil see around .5%

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: equivalent THDv

(OP)
Thanks

Yes, transformers are loaded (40% for 1st one, 50% for 2nd one) and supply different gears, so as you said, nothing in commom except primary voltage. Unfortunately, no meters on the 13.2kV side....

My guess is less than 1%, but I was wondering if any calculation method (even approximation) exists.

RE: equivalent THDv

You may review what are loads?

Are there predominantly non-linear loads (such as UPS, VSD, thyristor controlled heaters, Fluorescent lamps etc.)in the transformer which has 2.1% THD?

As such 2.1% at 415V is not a THD level which is a cause for any concern as the tolerable level is much higher.

RE: equivalent THDv

Could part of the harmonic distortion be originating on the supply grid?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: equivalent THDv

(OP)
Sorry, I was away a few days.
Loads are mainly motors driven by VSD.
I'm not really concerned by the value itself, as it remains under 3%.
My concern was to try to calculate the value on the 13.2kV side. But it seems clear we can't.
Thanks

RE: equivalent THDv

As far as the %ge harmonic current distortion is concerned, it is same at 415V and 13.2kV side.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources