In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
(OP)
I am working with a condo project located in CA in the Sierra that has seen huge roof snow overload conditions this winter. Roof was designed for 135 psf of snow (about 5.4 ft of snow) and had 12 ft of snow on it when the beam failure was noticed. The 8x14 roof beam has a longitudinal crack at the neutral axis of the section almost the full length of the beam. Fairly deep too. Not all the way through but almost. No obvious problems with mid-span bending failure, just horizontal shear.
I'm trying to work out some kind of minimalistic way to retrofit vertical shear reinforcement (something like the shear ties in a concrete beam) into this wood beam.
Is that a realistic approach? Any ideas? Any products?
I'm trying to work out some kind of minimalistic way to retrofit vertical shear reinforcement (something like the shear ties in a concrete beam) into this wood beam.
Is that a realistic approach? Any ideas? Any products?






RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
There were horizontal cracks in the beam similar to what you describe. The solution we came up with was to drill a series of vertical lag screws up into the bottom of the beam such that the lag would extend past the crack and take the horizontal shear force in the beam. Sort of a set of internal pins tying the top and bottom sections together internally.
Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
Dik
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
I have access to use epoxy or polyurethane. Are there products with strength ratings?
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
I have used epoxy injection on past projects to provide structural 'crack' repair to wood beams similar to what you would typically do with concrete crack repairs. A low viscosity resin of less than 500 cps would fill fine cracks. If the crack width is larger than 1/8" you may consider a paste resin. Both would provide similar structural bond, tensile and compressive strengths.
Lags screws, as JAE stated, coupled with epoxy injection, would be a 'belt and suspenders' approach.
Polyurethane has no structural strength - mainly used to seal cracks from water ingress etc.
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
Did you calculate the snow load required to fail the beam in shear and bending - which one governs?
The 8x14 is solid sawn - right? It may have had a seasoning check pre-existing which reduced it's capacity in H shear.
I agree with the repair methods with lags & epoxy, but you need to verify the capacity of the beam and reinforce it if it is marginal. Shouldn't get much resistance from owner, since it "failed" before.
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
Feet of snow is not too reliable a measure of weight.
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
It is an exposed interior beam by the way, so the fix needs to look good too.
I have not had a chance to calc any of the loads in the beam yet. I am triaging distressed structures all over town right now for temporary (get through the end of winter) shoring. This one is a bit lower in urgency than some others but I wanted to research options before I spec'd a fix. We put a temporary shoring post under the beam mid-span and removed the snow off the roof, so I bought myself some time. I am looking for the most effective, least intrusive long term fix for this. You guys are always a good resource on what has worked well in real life.
I have an email in to 3M's technical staff for a high strength wood-to-wood structural bonding agent recommendation. I thought I'd calc the shear flow value and try to find a bonding agent with enough margin to work for the loading condition. I am also researching Fastenmaster, that has some good long lag-style woodscrews that might work. Their shear values are higher than regular lagscrews. Once I calc the shear loads however I might have to go to big thru bolts if the loads are high enough.
Thanks for the help!
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
What if this happens again and one collapses and kills some people? I think the lawyers would have a field day with it if there is already evidence that you knew they saw a snow load in excess of their design capacity (if I am reading your original post correctly)
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
I was thinking epoxy, then clamped, then angled lags added, plus some oak dowels epoxied in bored horizontal holes, oriented similar to the keys shown in the link above along the bonded split.
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
https://4.bp.blogspot.com/-o7UBnJUh2Vk/TzwPuAWZGGI...
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
We got several rain on snow events in January and February and the roofs are carrying serious ice layers under very saturated snow. From what I have seen 12-18 inches of solid ice at the eave is pretty typical. That doesn't include the very substantial weight of huge dripping eave icicles. That is an additional 57 - 86 psf minimum of roof load to a roof already carrying many feet of snow. Its also cold now and nothing is melting off. Very atypical for this region. The snow pillow measuring station says the snow is weighing 19.5 lb per vertical foot. But that doesn't include roof ice.
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?
RE: In-place retrofit/reinforcement for sawn lumber DFL roof beam failed in horizontal shear?