ZCT setting in ungrounded systems

ZCT setting in ungrounded systems

ZCT setting in ungrounded systems

(OP)
How do you set the current setting coming from the ZCT? Does ZCT produce any secondary current at all?
If it is a single feeder in a power system (against the radial) the ZCT balances the charging current 3Ic in case of single phase to ground fault and produces zero flux. On the other hand, in case of radial feeders there would be some small current from the ZCT? Has my understanding right?

RE: ZCT setting in ungrounded systems

@charz,
The trick there is to wire the shielding earth wire back through the ZCT. Keep in mind that any earth wire should never pass through the ZCT. That way the summation of the currents flowing on the phase conductors in the ZCT does not include the ground currents flowing in the shielding screen.

RE: ZCT setting in ungrounded systems

(OP)


My question is how to make the ZCT sense the fault current even if it is very small

RE: ZCT setting in ungrounded systems

Use three CTs or three PTs connected in grounded wye.
Secondaries connected in broken delta. (Open delta in IEC land?)
The CTs will show the unbalanced current to ground.
You may use a loading resistor to convert the current output into a voltage output.
The PTs will show any event that causes the voltage to ground of any phase to drop.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: ZCT setting in ungrounded systems

(OP)
Hi Waross,

Isn't using residual connection of 3 CT's same as using ZCT?

RE: ZCT setting in ungrounded systems

charz (Electrical)

It looks like the application of protection scheme is not appropriate to the system, i.e; ungrounded system.

Detection of earth fault becomes difficult using a ZCT and a non-directional relay. The capacitive current introduces some a 90° phase shift. This confuses many people. I would suggest you to go with the time tested ground fault detection and protection scheme for the ungrounded system.

At least in the IEC world, the ungrounded systems are now becoming rare and used only in some special cases.

RE: ZCT setting in ungrounded systems

Great illustration, which shows an obvious answer. Move the CT so it lies between the cable capacitance and the fault. Since this may be a bit impractical, a voltage based scheme may be in order.

RE: ZCT setting in ungrounded systems

For ungrounded systems with only 1 feeder is true that the ZCT (window transformer) do not see earth fault current because the current of the faulted phase is the sum of the other phases (opossite direction) and always the ZCT see zero amper. (IEEE papaer "Considerations for ground fault protection in medium-voltage industrial and cogeneration systems D.J. Love and N. Hashemi)

For the small network can use the 3V0 element for detection (PTs connected in grounded wye indicated by Waross).
The phase to earth capacitive charging produces more high values of residual voltage (3V0) (opposite to big network that for the same fault type have low values of 3V0)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources