FUEL STORAGE TANK VENTILLATION
HELLO,
WE HAVE A FUEL TANK WITH AN INTERNAL FLOATING ROOF AND A FIXED ROOF ABOVE, IN ORDER TO MAINTAIN ZERO EMISSION TO THE ATMOSPHERE CAN WE USE VACUUM BREAKERS FOR INBREATHING AND WHEN OUTBREATHING TO CONNECT THE OPENINIGS TO A HEADER TO A THERMAL OXIDIZER, I MEAN THAT WE WILL DIVIDE THE PERIPHERICAL OPENINGS IN THE FIXED ROOF FOR VACUUM BREAKERS AND FOR CONNECTION TO THE THERMAL OXIDIZER.
IS IT OK ACCORDING TO API 650 AND API 2000?
REGARDS,
ROKER
REGARDS,
ROKER
RE: FUEL STORAGE TANK VENTILLATION
Dejan IVANOVIC
Process Engineer, MSChE
Conservation vents, not vacuum breakers are used. Consider the use of a 2nd vent (at higher pressure) to atmosphere to protect the tank
Your issue is almost certainly that the tank is only designed for "atmospheric" pressure which leaves very little available pressure (4 inches of water guage) to blow the vapour out to any equipment located some distance away. you can end up with massive ducts and if the oxidizer creates any sort of back pressure, your idea won't work I'm afraid.
So sounds like a good idea, but unless your tank is designed for a higher pressure, it is practically impossible.
So check API 650 and check the design limits of your tank. if you get this wrong you will destroy your tank very easily. Do nothing without getting this properly designed and approved by competent, experienced tank designers.
The vent outlets are collected to a thermal or catalytic combustor.