sand trap louvers calculation
i have 3200 CFM must go through sand trap louvers ? i need calculation and how to calculate it ?
RE: sand trap louvers calculation
Manufacturer should provide the free area(s) for their louvers and a maximum rated velocity to prevent 'sand'(?) penetration.
They should also provide pressure losses through their louvers as the functions for this will vary depending on the louver geometry.
should be selected for a maximum free area velocity
of 600 feet per minute (FPM).
Example:
Given:
Airflow: 2658 CFM
Assumed free area velocity: 600 FPM
Calculate for free area, neck size and pressure
drop.
1. Free Area = 2658 CFM / 600 FPM = 4.43 ft².
2. From Free Area Chart the outer frame size is
48in X 48in ( W1 X H1 ).
3. From Table 1 neck size is 1100mm X 1100mm
( W X H ).
4. Pressure drop = 0.151 in. W.G. (38Pa).
Note:
For optional screens the pressure drop is
additive and to be calculated separately.
