shear check for plate elements
where should i compare the values of SQx and SQy? is it only for fv = Vc/bwd?
what if concrete shear capacity is not enough? what can i do?
how can i design link bars to increase shear capacity?
RE: shear check for plate elements
Be careful how you interpret results. You may get a very high shear at a very isolated location, but, in my opinion, that does not mean the concrete will fail in shear. I occasionally do some averaging of shear results to get a more realistic shear value.
DaveAtkins
Keep in mind though: you will need to (either) factor up the stresses or factor down the allowable to account for the fact that you are getting stresses based on the full thickness of the element. In actuality, the stress will be higher based on the fact the thickness that resists the shear stress will actually be the depth to re-bar ("d") rather than the full thickness.
@DaveAtkins is averaging shear values an acceptable method? is there any provision from any code that allows us to get the average shear for our design? if yes, then i think it will help me on my current design project that only fails in shear when compared to Fv.