Proof Loads - Post-Installed Epoxy Anchors

Proof Loads - Post-Installed Epoxy Anchors

Proof Loads - Post-Installed Epoxy Anchors

(OP)
Hello Everyone,

I am trying to determine proof loads for some post-installed epoxy anchors using Hilti HIT-RE 500 V3 epoxy. Previously I had found this documentation from OSHPD from 2008 (which seems to be an interpretation of the CBC):

Test loads should be greater of 2x maximum allowable tension load or 1.5x max design strength of anchors. But should not exceed 80% of nominal yield strength of anchor (0.8*Fye*Ase).

I recently reached out to Hilti for their recommendation on it and received this recently revised segment of AC308 13.3.4:

Test loads shall not exceed the lesser of 67% of the bond strength (uncracked concrete and accounting for edge distance and embedment) or 80% of the nominal yield strength of the anchor.

To me, the requirements from AC308 make more sense but do not account for other possible limiting factors in the design(e.g. concrete break-out strength could control over bond strength).

What is the industry standard for proof load testing? What do you guys spec for proof loading? Thanks in advance.

Peter

RE: Proof Loads - Post-Installed Epoxy Anchors

We don't proof load. We require continuous special inspection during the installation. When we have required them in the past we used similar language to the OSHPD requirement.

My understanding is that the proof load doesn't correlate well as the test is not dynamic and the concrete is not cracked during loading. Therefore, the values are not very representative of the design conditions.

RE: Proof Loads - Post-Installed Epoxy Anchors

I agree....Continuous Special Inspection

Cannot forget Boston's Big Dig Tunnel Ceiling Collapse.

Link

Jeff
Pipe Stress/Structural Engineer
www.xceed-eng.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources