Lateral "F1" Loads for Simpson Face-Mount Hangers?

Lateral "F1" Loads for Simpson Face-Mount Hangers?

Lateral "F1" Loads for Simpson Face-Mount Hangers?

(OP)
Please see attached...

https://res.cloudinary.com/engineering-com/image/upload/v1487185632/tips/Lateral_F1_Inquiry_hx6bzx.pdf

Is there ANY way to obtain ANY lateral "F1" load from Simpson face-mount hangers?

I've discussed this with Simpson in the past and they simply say that they have not tested these components for a lateral application. I understand this, but, it does not help my situation.

Is there an ESR report that might provide this?

Is there another option?

Do I HAVE to provide an "additional" hurricane tie?

Another thought is to use (2) 10d toe-nails, (1) each side of joist or LVL in addition to the face-mount hanger.

I only need to resist 122 LBS at each joist.

Any suggestions?

RE: Lateral "F1" Loads for Simpson Face-Mount Hangers?

Does the toe-nail type holes on their hangers not provide you the capacity you require?

RE: Lateral "F1" Loads for Simpson Face-Mount Hangers?

(OP)
jayrod... after going through all the necessary adjustment factors, I can barely obtain the 122 that I need.

Does it make sense that, when considering using toe-nails for lateral resistance through a Simpson hanger, I can only use 1/2 the toe-nails - those on the preceding side of the hanger - since the other side, laterally, would be in withdrawal? I suppose I COULD apply the toe-nail withdrawal factor also, if necessary.

Therefore, the Simpson hanger allowable gravity of 1965 LBS x 0.64 (adjusment factor for replacing 16d x 3.5 with 10d x 1.5) = 1257 LBS minus actual gravity of 890 LBS = 367 LBS times 1/2 the toe-nails = 183 LBS x 0.83 (toe-nail factor) = 151 LBS > 122 LBS. I barely made it! Did I miss anything or did I over-analyze?

RE: Lateral "F1" Loads for Simpson Face-Mount Hangers?

Would you see full lateral with full gravity? That would be a little bit of additional capacity in the back pocket.

I would be inclined to say you're putting in more effort than most.

RE: Lateral "F1" Loads for Simpson Face-Mount Hangers?

BSVBD:
Read your other thread, same TJI roof detail. I lost the face mounted hardware, and expect the hardware saving in the form of a check. Use screws to attach the TJI to the doubled 2x6/2x4 studs. They should be good for 122lbs. in tension and the opposite direction is wood on wood compression perpendicular to the grain.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources