Calculate Drying Time of Nylon Parachutes
I'm designing the HVAC system for a parachute drying tower. What equation can I use to estimate drying time? I know the amount of water in the parachute, the temperature and CFM across each parachute, and I can approximate the exposed surface area. I've looked at various equations for water evaporation but none appear to take into account the convective air flow across the surface. One promising way would be to calculate the BTUs required to evaporate the water but I don't see how that could include the air flow. In my mind, higher air flow would result in quicker drying times. One formula I found involved the difference in vapor pressures between the water and the vapor pressure of the air but again, this seemed to be applicable to air at a standstill. Still another was a formula for evaporation of a pool of water which did include water temperature, air temperature, surface area of pool, and CFM. However, these resulted in unrealistically short drying times. They also assume the water is freely on the surface versus entrained in a fabric, so there may be some capillary action involved and there will be numerous folds in the parachutes since they are hung from the top of their canopies.
Anyways, I have virtually all of the data since I am designing the system but I do not know of a formula or empirical data regarding nylon (or other fabric) drying rates.
If it matters, our system is 100% outside air which will be heated to 120 F, ducted into the space at the bottom of the tower, and exhausted out of the top of the tower. I do know outside air conditions if humidity of the air plays a role.
I appreciate any ideas or advice.
Thanks!
Thanks!
RE: Calculate Drying Time of Nylon Parachutes
Mike Halloran
Pembroke Pines, FL, USA
That will give you a starting point for the theoretical energy to evaporate the theoretical mass of water.
Time to remove that much water remains very tightly linked to how the chute is spread out to expose the maximum surface to the dry air while NOT allowing it to deploy (billow out like a sail, or frankly, a parachute. Try a loose mesh bag with the parachute bags in a loose pile. Is tumbling the bags practical?
These parachutes are very large so tumbling is not practical. The design of suspending individual parachutes from hooks on hoists by their canopies and allowing them to hang down to the floor is industry standard. Water run-off and evaporation takes place during the drying time. I agree that from a practical perspective, increasing surface area is ideal and controlling airflow so that the parachutes do not billow is important. Typically, the parachutes are shook out about every hour to remove loose water and to introduce more of the chute to open air. Since these are suspended from the centerpoint of their canopies, there are numerous folds in the fabric while suspended.
I am designing the system, so I can control the surface area and airflow. Assume I can control the process as if I were in a laboratory setting. What reliable equation can I use to estimate evaporation (i.e., drying) time? I understand that theoretical and practical may vary but I am trying to get a basis.
A Google search on
equations for drying fabric
produced a bunch of stuff that looked relevant to me.
Mike Halloran
Also don't forget that there are lines attached which are thicker and can take a lot longer to dry out than the canopy. As an ex skydiver I have personal knowledge that is the lines which take the time to dry, not the rather thin canopy.
In terms of your question I think there is simply too many variables on how the fabric is hung and how air flow travels past them to come up with any sort of formula. I think your only way is to do some testing of humidity levels of air entering the building versus exit and plot the decline to show when drying has been completed. You might then be able to experiment with different ways of hanging or shaking to see which is best.
Start overall with your amount of heat to evaporate the weight of water then add in an efficiency factor of say 20 to 40% and work from there. Given the number of these apparently built there must be a ROT on how long it takes to dry 30 canopies. Just need to find the grizzled old guy that's been doing it for 30 years and can still talk sense. ....
Regarding the heat required to evaporate the water, allow me to ask a dumb question. Isn't the heat output from AHU energy measured in BTUs? So the air flow rate, whether stagnant or 10,000 CFM isn't accounted for because the only energy is the heating element in the AHU. I agree there are numerous complexities and hence why you suggested a generous efficiency factor. But still I'm trying to differentiate these parachutes from being in an oven versus convection oven, if that makes any sense. The air flow is going to have a dramatic impact on drying time. I feel like I would need to use a convective heat transfer equation (accounting for air speed) and set it equal to the heat of vaporization of the mass of water. This still however wouldn't account for humidity since the vapor pressure difference between the water in the chute and the relatively low humidity air is the energy which dries materials. While this could account for the heat (since hotter air can better absorb moisture, this greater vapor pressure differential) this still wouldn't account for air flow rate.
The incoming air has some properties, temp, RH, and corresponding enthalpy. the outlet air will be cooler and wetter.
You need to move enough air so that the outlet air does not reach 100%RH.
I would start with some Google searches, and then trial calcs based on say 16hr dry time (overnight) and see if it makes sense to remove that much water in that time period.
The lower the RH of the inlet air the more driving force there is to overcome the water stuck in the fabric.
Sadly my skydiving days were a long time ago, but even then we tried to keep our canopies dry as it was a complete pain to dry them, especially the lines, which was my point. I only ever deliberately jumped into water twice and it took days of drying in my living room to dry the bloody thing out.
The type, size and number of canopies you're looking at looking at would appear to me be wholly military application. I'm surprised you don't seem to have any real specifications or design basis to work from.
I get that you're trying to do this scientifically, but the air volume is so high and velocity you're looking at in the drying shed will be so low that I can't see it (velocity) making a big difference. The last thing you want is for any of the canopies to do anything other than gently drift a bit in your gentle wafting air flow through the shed.
In essence all you're doing is blowing warm air into a building and presumably letting it out at the top. I would have thought de-humidifying it would have helped, but clearly adds to the cost and if they are happy to leave them there for 24 hours and it's all dry then what's the issue?
Getting something "dry" is such a vague term and the density of the items is quite variable (canopy to lines) that you're on a hiding to nothing without doing some tests on an existing facility to make sure you're not over or undersizing your heater.
Contract someone who does this for a living to design the process and you can select the equipment.
Like these guys maybe: http://www.paradrysystems.com/
I would have thought you were looking at 12 to 18 hours to do this for a bunch of canopies all hanging next to each other getting shaken out at regular intervals.
Personally I think you want to look at lowering the incoming RH by a bit of de-humidification so you don't roast the packers as they shake the canopies and it would also account for any rally humid days you get on site.
http://www.apricus.com/upload/userfiles/downloads/...
Recirculating the air is tricky because the air would need to be blown back down, outside of the building in a very large insulated duct, then recirculated through the AHU for moisture removal. It seems like a mess and I'm not sure that much energy would be saved in the long run. If I were to do this, I would probably not heat and just ventilate/dehumidify the space. Keep in mind the entire tower (say 35 ft x 35 ft) is acting like a large duct for air flow.
You know how much water you need to remove, so a little math tells you how much air you need to flow. I would assume that real amount is double or triple this because of the factors already mentioned.
Does this total volume of air over 12-18-24 hours sound reasonable? Could you manage those flows?
I wouldn't try recirculating, but if the incoming air was very humid I might look at dehumidification. It uses a lot of power but you can at least capture some it in helping warm the air a little.
where
gh = amount of evaporated water per hour (kg/hr)
Θ = (25 + 19 v) = evaporation coefficient (kg/m2h)
v = velocity of air above the water surface (m/s)
A = water surface area (m2)
xs = humidity ratio of saturated air at the same temperature as the water surface (kg/kg) (kg H2O in kg Dry Air)
x = humidity ratio air (kg/kg) kg H2O in kg Dry Air
Link
So first problem is this is an empirical equation for pools (open water surfaces). Problem two, I have no idea what this equation comes from. Problem three, I am somewhat confused by the two humidity ratios. Is xs the fully saturated air at 120 F? And x is the humidity ratio of 0.4% MCDB air heated to 120 F, as taken off the psychrometric? [0.4% MCDB 80.2 at 76.0 DP]
Based on an estimated exposed area of 43.8 m2 per chute (3 ft dia x 50 ft length), a velocity of 0.02 m/s, a humidity ratio of saturated air of 0.08 and a humidity ratio of air at 0.017, I got 70 kg/hr of evaporation. Our biggest chute holds 175 gal of water, so this equation (if I'm using it correctly), predicts the chute will be dried in just over an hour. Even before a heavy safety factor, that seems high.
If any kind souls want to let me know if I'm using this formula correctly, I sure would appreciate that.
You need to take your worst case inlet air (hot and humid) and figure out its moisture content at 120F.
The exhaust air won't be at 120F, it will be a little cooler, so you will need to assume some evaporation rate and do some iteration.
Does anyone think this is a valid approach?
You need to meet both criteria, and then use a multiplier of 3 or 4 on the time.
Still, I don't think this approach is sound because at ambient temperatures the chutes will still evaporate with no heat and no airflow. The chutes will evaporate faster with no heat and a high airflow rate. They'll evaporate faster still with heat and a high airflow rate.
For example, for a sheet hanging on a clothesline in the wind, there is energy from the ambient temperature of the air, plus the convective force of the wind blowing against the sheet. How would you calculate this dry time? Then take it a step further. What if you were in Arizona on a 110 F day with low humidity and a gentle breeze? That is what I'm trying to solve. If I can do that, I can apply it to my drying tower.
Part of me thinks this is a convective heat transfer question, but if the water in my chutes is the same temperature as the ambient air, there is no delta T, so I don't know how to model the evaporating water as heat transfer.
Air velocity changes the amount of heat that can be transferred; typically, the faster the flow, the more heat is transferred. However, since your air flow is never monoatomically thick, the air that's farthest from the parachute does nothing in the heat transfer process and conveys nothing away from the parachute. This is why there's a fudge factor of 3 or 4.
TTFN (ta ta for now)
Let's say that given your inlet air conditions and heating to 120F that each lb of water removed will be enough to saturate 1,000 scf of air.
Now if you are trying to remove 800lbs of water total, that means that you need at least 800,000 scf of air, and more likely 2.5 million scf to allow for lack of mixing and such.
Now look at the energy balance, using the heat that it takes to evaporate water (phase change) and the heat input into the air. Heating with your heaters how much air will it take to deliver that much energy? Is it more or less than the number above? you need to work with the larger one.
In reality if you heat the air from 90F ambient to 120F, I would assume that the exit air after passing over the chutes is 110F.
You heat the air for two reasons, one to deliver energy to speed the process and also to supply unsaturated air to allow for transport by evaporation. If you supplied saturated air at 200F you would get no evaporation, there is no place for the water to go. Likewise you could supply very dry (-20F dew point) air at low temp (40F) and you would get drying, but it would be slower than using warm air.
You're looking at it from a heat transfer / thermodynamics side where as what you're actually doing is drying something.
Part of the problem is how dry is "dry". Not easy to define in a technical sense.
As the water transfer is based in part of difference in humidty levels between the item 9 fabric and lines) and the air, then maximum water transfer is at the beginning, but then drops off as the RH / "dryness" of the fabric approaches the RH of the air.
Your statement " at ambient temperatures the chutes will still evaporate with no heat and no airflow." is not, IMHO, correct. If you simply strung the chutes up in the drying tower and then sealed it off you'd never get the chutes dry.
If you just add heat and no airflow then you would simply end up with a steam room / sauna
Just add airflow then chutes will slowly dry until they reach equilibrium with the RH of the air passing through them.
So if the drying time is not specified by the client, but you want to aim for a certain value (T hours) then I would go for the overall thermal quantity and then add a factor of 3. It may mean on some days it will take your time T - 1/3 or on a humid day T + 1/3. Is T that important?
Reserve some space for a de-humidifier and all you bases are covered.
Also can you explain "My initial thought was also to dehumidify the air (either subcooling or desiccant wheel) then heat it but that is a big waste of money." Why is it a big waste? If you include the waste heat from the process in the tower, you end up with warm dehumidified air. Where's the big waste in that?
Regarding dehumidification, I meant I'm doubtful the energy put into dehumidification (and capital cost) would justify the assumed improvement in drying times. If we don't have a reliable way to calculate drying time, I doubt we have a reliable way to calculate the effect of dehumidification, versus simply heating the outside air. And even if we took the 0.4% dehumidification data, the dehumidification improvement would only be applicable 1 day a year, and that's if they were even washing/drying chutes that day.
For an attempt to quantify dehumidification and reheat, versus simply heating, here goes. On the most humid day, the humidity ratio (lbs moisture per lb dry air) is 0.018 compared to the air moisture holding capacity of 120 F air of 0.08 lb moisture per lb of dry air. Cooling to 50 F to wring out some moisture and reheating would result in a humidity ratio of 0.008. So if drying performance is directly related to the delta between the humidity ratio of the air in the tower and the moisture holding capacity of air, then drying performance would be improved by max 16%. And again that's only on the most humid day of the year. The rest of the year it would have less effect and in the winter, no effect.
I will admit that if we were using DX cooling, there is potential of heat recovery from the hot gas, so that would help some of the "wastefulness" I was previously referencing. But I'm not sure what you mean by waste heat from the process in the tower. Do you mean a heat exchanger at the exhaust to pump hydronic heat back down the AHU? Blowing the air itself back down is impractical but there is probably an opportunity for heat recovery from exhaust. However, this would increase cost and system complexity.
I should clarify this is a 100% OA system. If the air was being recirculated, I would agree dehumidification is required because where else will the water go?
I would also like to point out that the air moisture holding capacity between 70 F and 120 F quadruples, which is why heating has such a dramatic effect on drying.
One issue with the 120F / 50C is the use of people every hour to shake out the canopies to ensure a good drying area given these things hang down in a straight manner.
Asking anyone to work for even a few minutes in that temperature is very uncomfortable and could be against regulations. If you've got 30- 40 canopies all strung up then that's not something which is going to take a minute only.
I these instances you are not going to get anywhere without some practical / existing system information. You should have a good start point based on the heat input required, but to get any more sophisticated you're going to need to benchmark this against existing drying systems, temperatures and air flow.
Or guess
Clothes dried on a line tend to get "crunchy" due to minerals in the water that acts as a "starch". You may want to rinse the chute in distilled water after washing. If drying time is not critical then it would be best to not use heat but only ventilation. If the humidity outside is very high, a portable dehumidifier can handle the load of drying a chute, along with circulation fans.
The second link doesn't seem to go to anything showing worksheets, unless you're referring to: http://www.bryair.com/download_pro.php?action=down...