For IBC 2006 TABLE 1604.3 DEFLECTION LIMITS, It states the limits for (S or W), in this case do I have to consider the effect of the wind load solely on the structure or I can calculate the deflection based on the criteria: D + 0.5L + 0.7W in Design Guide 3 ?






RE: For IBC 2006 TABLE 1604.3 DEFLECTIO
RE: For IBC 2006 TABLE 1604.3 DEFLECTIO
RE: For IBC 2006 TABLE 1604.3 DEFLECTIO
RE: For IBC 2006 TABLE 1604.3 DEFLECTIO
RE: For IBC 2006 TABLE 1604.3 DEFLECTIO
DaveAtkins
RE: For IBC 2006 TABLE 1604.3 DEFLECTIO
RE: For IBC 2006 TABLE 1604.3 DEFLECTIO
That's all, thanks
RE: For IBC 2006 TABLE 1604.3 DEFLECTIO
Read the Appendix C Commentary in the back of ASCE 7 for wind drift guidance---again, not Code-mandated, but something designers are at risk if they don't consider. ASCE does suggest your D+0.5L+W. There is plenty of discussion here about wind drift. H/400 is the most common value, although I have my doubts how often this is truly reached.
Wind drift is primarily influenced by the connection/jointing of the nonstructural elements such as precast, brick, glass, etc. If the joints can handle rotation without leaking water, a higher drift is justified. This is a very difficult parameter to pin down, however, so the cost savings should be substantial if less than H/400 is sought.
When I do wind drift, as a general rule I use 0.7 (0.42 of ultimate; 10-year MRI) W and design for H/400. I ignore D and any uplift wind since they are vertical forces and therefore don't have a significant influence on lateral drift.
RE: For IBC 2006 TABLE 1604.3 DEFLECTIO
They have a nifty table outlining all sorts of drifts based on exterior cladding and supporting frame.
This is not code required in the U.S. for wind.