ERV instead of HRV?

ERV instead of HRV?

(OP)
I know 'if you use a heating system more often than air conditioning, you need an HRV. If you use the air conditioning more than a heating system, an ERV is recommended'.

But is it OK to use ERV for either heating season or for cooling season? Any reason for us to select ERV or HRV? The reason for cost or for any other reasons? If there is no difference regarding the cost, can I use ERV for any locations in cold or humid? Since ERV has more benefits: recover both the heat and the enthalpy.

Please let me know if I can use ERV all the time for my projects everywhere rather than HRV.

RE: ERV instead of HRV?

Please explain what your TLAs mean.

Mike Halloran
Pembroke Pines, FL, USA

RE: ERV instead of HRV?

Not sure if you just repeat what you read somewhere, but ERV recovers full enthalpy inc. latent energy (moisture). you can use it in heating only applications.

RE: ERV instead of HRV?

Did you perform calculation to show you how much latent heat you can get in heat-only application!?

RE: ERV instead of HRV?

First off ERV or HRV is only beneficial if you have large amount of exhaust such than large or 100% outdoor air is required. ERV or HRV would be the choice instead of glycol run around heat recovery coils if the exhaust discharge location can be made adjacent to outdoor air intake location. Use ERV if you need to recover latent heat. The latest ASHRAE Hospital HVAC Guideline do not allow use of ERV or HRV because of possible contamination of the outdoor air by the exhaust. There would be fan energy penalty for pressure drop through the ERV/HRV and upstream air filter to protect the ERV/HRV. Automatic controls and provisions should be provided t0 prevent overheating of AHU intake air and frosting on the ERV/HRV.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close