Footing Rebar - 2 Matts?
The only time I typically specify (2) rebar matts for footings is when I'm dealing with pre-fab metal buildings with high uplift.
In this conventional building of joist and girders, I'm not anticipating uplift to be as much a requirement, if at all.
My 2-way punching shear forces me to go with 18" thick footing.
At what footing thickness might it be necessary to add a 2nd matt? And why?
RE: Footing Rebar - 2 Matts?
Wouldn't you put a top mat in for temperature steel?
1) with only bottom steel, you may get bottom side restrained, differential shrinkage curvature in the footing leading to cracking at the top. Flexure, when present, would tend to close those cracks. And I'm generally not too concerned about the cracks anyhow unless the footings are in an especially corrosive environment.
2) at some depth, perhaps the integrity of the sides of the footing becomes an issue and it would be best to have a continuous "basket" of reinforcing around the whole thing. This I don't buy at all.
In a large raft foundation it seems like positive moments would incur if the reactions on the foundation is large. A typical footing is one thing but a massive thick raft foundation I would replicate the bottom flexural steel.
Dik
http://www.ccaa.com.au/imis_prod/documents/Library...
A pile cap as you describe is similar to a continuous concrete beam / floor system with tension forces alternating between bottom of cap/slab at "mid-span" and top of cap over the pedestal supports.
This is a different situation that i will defer to the apparently more experienced elaboration of hokie... please...
Did you carefully read that Leftwow is inquiring of a 100' x 100' cap?
I must be misunderstanding something...
Will there not be tension in the top half of the 2 foot thick cap requiring rebar in the system of which Leftwow inquires?
BSVBD has answered for me. Surely a pile supported mat slab, or an earth supported mat slab for that matter, of those dimensions, would have both top and bottom steel. My answer was about leaving out top steel where it has no benefit, and where I know plastic settlement cracking is probable.
rapt's suggestion of a mat for workers to stand on has merit, but there are other ways to do that. That is in the nature of constructability, what some here call "means and methods".
I don't see where any offense was implied.
It appears as though you were getting credible and considerate answers to a serious and legitimate question.