Trench Excavation Shoring.

Trench Excavation Shoring.

(OP)
Looking for input on a timber trench excavation shoring.

The trench is up to 12' deep and 5' wide. The soil is "type B" and is mostly sand. The site is to be dewatered during excavation.

The vertical and horizontal spacing is 4' between cross braces. All material is lumber.

My calculations show the 3x10 horizontal lagging, 3x10 uprights and 6x6 braces should be OK. From what research I've done online most lumber shoring use upright planks for the "sheathing" or a soldier pile and horizontal lagging design.

See attached image for reference.

RE: Trench Excavation Shoring.

Assuming you are asking for a check on design adequacy, well this site is not to be used for design as I understand it and using any design verification from here may well not be of value in case of some failure on the job. I'd opt for a commercially made trench shield.

RE: Trench Excavation Shoring.

OG:
In these environs, trench boxes would normally be used. In particular if 12' deep.

Dik

RE: Trench Excavation Shoring.

daca02, you can check your timber trench shoring design with information in OSHA's trench safety manual.

www.PeirceEngineering.com

RE: Trench Excavation Shoring.

Agree with Dik, it would be much safer and easier to go with a trench shield/box. Typically they are 8' tall and can vary in width and length. The reason for the 8' typical height is for transporting without an over-width permit. They are easily rented for short term and come with the required engineering certifications. For your case we would get the 8' tall shield and then slope the top 4 feet. Also, as PEinc pointed out, OSHA has a good section on trench shoring, which would be the governing safety agency.

RE: Trench Excavation Shoring.

If the trench has a number of relatively closely spaced crossing utilities, a trench box may not be suitable. In that case, vertical timber shoring might be a better shoring method.

www.PeirceEngineering.com

RE: Trench Excavation Shoring.

If I remember correctly you can stack one trench box on top of the bottom one, however, double check on my statement as regulations may have changed.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close