ASCE Substation Structure Design Guide
The ASCE substation structure design manual has its own load factors and combinations which are lower than the ASCE7/IBC. I understand why they are lower but I'm wondering what legal grounds an engineer has to use them since the document is a guide and not a code. We work for an electrical engineer and design the steel support structures and foundations for their substations. We just want to make sure that if there damage from a weather event that we're not drawings additional liability by using the reduced loads. I have tried reading both the IBC and a few state codes as well as the NEC and NESC and it's not clear to me which documents apply to substations.
RE: ASCE Substation Structure Design Guide
Longer answer: it comes down to the scope and applicability of each standard. Just because ASCE or IBC publishes a standard doesn't make it the governing code for any given project. That happens when:
1) The document states that your project type is within its scope of intended use (side note, IBC's scope makes me laugh)
and
2) Some government agency (often in a local building code) states that projects of type X should conform to standard Y.
Sometimes 2) doesn't happen (especially in construction or industrial applications). In this case, your liability is typically limited to the prevailing standard of care provided by other reasonable and qualified engineers. For substations, this is where you fall -- there's a lot of precedent for using ASCE 113, and I've never heard of another code being legally required instead. (You should double check this with your specific client, but sounds like you already have looked into it).
I might be getting mixed up, but my memory was that NESC only applied to power structures outside the substation fence. (small caveat, we'd also use it for the deadend, since it saw loads from outside the fence).
But I've never seen it done.
www.SlideRuleEra.net
www.VacuumTubeEra.net