Generator controller settings?

Generator controller settings?

RE: Generator controller settings?

It looks like you have an inverse curve combined with a definite time one. Inverse has a factory default pickup of 105% with a time multiplier of 0.27. Def Time has pickup of 110% with a 10s time delay. I do not know ETAP that well but I am sure it has relay trip current curves you could call up from an ETAP model for your relay. These then get displayed as a TCC curve, displayed on the SLD, etc.

RE: Generator controller settings?

The inverse curve is an IEC Standard Inverse type judging from the constants. Pretty much any of the European numerical overcurrent relays will have both IDMT and DT settings which use the IEC curve.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources