Truss Heel Blocking
6

Truss Heel Blocking

Truss Heel Blocking

(OP)
I know this topic has been discussed in quite some depth in previous discussions. However, I would like to get some more input regarding raised heel trusses and what you have seen done by the truss manufacturer in your local areas with regard to supplying pre-manufactured heel blocking.

Most of the work I've done or at least seen constructed in my area tends to be non-raised heel trusses with bird blocking similar to the two examples below:



However, lately I've seen a couple jobs with fairly significant raised heels (12" - 24"). I'm not sure if this is a trend but in one case the truss plant supplied little frames for between the trusses, do you see a lot of this in your area? If the raised heel is too high then a solid 2x block is not practical in my opinion, what do you do in this case, shear panels?

A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com

RE: Truss Heel Blocking

(OP)
With an 18" heel the heel block is not practical:



Even though, structurally it is probably optimal.

A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com

RE: Truss Heel Blocking

With high heels (e.g., 24"), I have typically detailed little shear walls between the trusses.

DaveAtkins

RE: Truss Heel Blocking

I've had some really large heels where I've just provided horizontal continuous 2x4 at the top of the heel and then diagonal 2x4 extending across at least 3 trusses from top of heel to bottom.

I will admit, most people in my area just ignore the rollover of trusses entirely.

RE: Truss Heel Blocking

I'm stuck in a "do nothing" market too. I'm quite impressed that others are getting the little shear panels though. I long to see one in real life.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Truss Heel Blocking

(OP)
From a structural standpoint the entire gable wind load is transferring into the roof (maybe some ceiling) diaphragm and then through these heel blocks into the shear walls below. I think one does need to consider them. I'm always specifying A35 clips between them and the double top plate of the shearwall.

I guess they are really no different than interior shearwall shear panels other than they are usually short enough so that a block will suffice. I will probably just use the same detail with a few minor modifications when the block height exceeds some set value (ie. 14"-16").

A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com

RE: Truss Heel Blocking

Oh the requirement for them is obvious. However as KootK is likely well aware, when we deviate from the local industry norm, we stop getting the phonecalls for the work.

I think most of the problem (in my area at least) is many of the existing homes from pre 1970's have essentially a 2x6 heel depth so rollover was a minor concern. And since the introduction of 12 and 14" typical heels the old engineers turn a blind eye, and the new engineers are never taught that it should matter.

RE: Truss Heel Blocking

Yeah, KootK is aware. This is something that I'd really like to see become a prescriptive code requirement. It puts engineers in a tough spot to have to choose between providing a real load path and staying in business. And it's not as though it's not an issue on pretty much every wood building.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Truss Heel Blocking

I have seen a couple scenarios:
1- general rule in our office is if the heal is greater than 24" and we are the project engineers we supply either blocking or small truss every 48" c/c
2- if nothing is shown on the client supplied dwgs that were sealed by a P.Eng, then we do not provide anything, but do place a disclaimer that diaphragm transfer to plates and shear wall is by project engineer.

As has been discussed above, if we were to include them as part of our package, we would calls from contractors stating that they haven't seen that before and won't put them in, couple that with the competitive market we are in, our competitors certainly don't do it so we are sort of stuck in doing what the industry does.

Cheers

paolo

RE: Truss Heel Blocking


Quote (Jayrod12)

Oh the requirement for them is obvious. However as KootK is likely well aware, when we deviate from the local industry norm, we stop getting the phonecalls for the work.

Ain't that the truth. I struggle with that everyday.


This is from the North Carolina code.... (see attached)

RE: Truss Heel Blocking

I'm guilty!

I've never provided any blocking or load path material from top to bottom chord.

We HAVE, on some occasions, specified the exterior, 7/16" OSB sheathing to be full height to bottom of top chord. Whenever we have parallel chord trusses that also provide a parapet, without overhang, naturally the exterior sheathing goes all the way up to top of parapet. That has GOT to account for SOME significant bracing.

I always specify an "H1" hurricane tie, which does have verticals both sides of the truss, but, i hesitate to think that that little bit of steel is the cure. It IS 2.75" of 18 gage.

I also would like to see blocking or other adequate material as a code requirement.

RE: Truss Heel Blocking

Quote (XR)

This is from the North Carolina code.... (see attached)

Go North Carolina! Seriously, that's bloody great.

Quote (BSVBD)

I'm guilty!

This topic always ends up feeling like a diaphragm blocking PTSD support group.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Truss Heel Blocking

While, we don't commonly work on high heel trusses, when we have, we specify to either provide full-height 2x blocking, pre-manufactured truss blocking or to sheath panels between trusses to form mini shearwalls.

RE: Truss Heel Blocking

2
(OP)
I like what I see with NC's code but I would prefer to bring the shear panel right up to the roof diaphragm:



Thoughts?

In my opinion the venting should come secondary to the structural concerns. Pop a few small holes in the sheathing below the 2x4 shear panel top plate, but not too many that the sheathing is overly compromised.

A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com

RE: Truss Heel Blocking

That is one option we use Medeek. Terry Malone's book has a good discussion on this approach.

RE: Truss Heel Blocking

Sheath or truss it and you're good structurally. Just need a plan for eave ventilation.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Truss Heel Blocking

(OP)
I'll have to open up Malone's book again, haven't looked at it for a while, that should be monthly mandatory reading.

A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com

RE: Truss Heel Blocking

Quote (KootK)

Just need a plan for eave ventilation.

Specify the top chord proper vent. The sheathing should only go up to bottom of top chord. The proper vent will break that sheathing plane.

Trusses i typically deal with, come with only the top chord cantilevering for the pre-manufactured overhang.

The soffit is framed by the contractor and then the vented aluminum soffit is installed.

Am i missing something?

RE: Truss Heel Blocking

I use the shear panel option between trusses on all my wood projects. It works well and they are pretty easy to construct. I'm actually kind of surprised that some of you are saying they would get balked at in your areas. As a warning, I've had a couple plan reviewers that will claim and that the shear panels between trusses are analogous to short shear walls and since the shear wall below is significantly longer, it triggers a vertical irregularity and a whole bunch of pain. Terry Malone agrees with them.

RE: Truss Heel Blocking

Quote (mike)

it triggers a vertical irregularity and a whole bunch of pain
Oh FFS, they should be happy anything is provided at all.

You have no idea the detailing norms around here. They'd make some engineer's skin crawl. Granted that's on the residential side of things, which thankfully my firm generally avoids except for preferred clientele.

RE: Truss Heel Blocking

I agree with medeek - bringing the shear panel up to the roof diaphragm allows additional nailing where the roof sheathing uplift is the highest. Drill round holes to get the appropriate ventilation area.

RE: Truss Heel Blocking

Quote (mike)

As a warning, I've had a couple plan reviewers that will claim and that the shear panels between trusses are analogous to short shear walls and since the shear wall below is significantly longer, it triggers a vertical irregularity and a whole bunch of pain. Terry Malone agrees with them.

FFS indeed. Now jayrod and I will be yet another step behind the state of the art.

Technically, those widdle shear wall panels need to be able to resist vertical shear or T/C on their sides to be in equilibrium. And, in many instances, you get that by fastening each panel to the last vertical of the truss such that vertical shear is passed across the truss from one panel to the next. Where that is the case, I would very much argue that the panels are just an extension of the primary shear wall rather than a whack of new, short shear walls. I guess, by the book, you'd still need to connect the mini-wall boundary studs at the far ends to the boundary studs of the primary shear wall. I would not want to be the first to specify that in my domain.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Truss Heel Blocking

(OP)
If you don't bring the shear panels up to the roof diaphragm then the top chords of the truss are being loaded in shear, I suppose it all works itself out somehow since I haven't seen any failure of roof from this but the load path seems more convoluted. I suppose one could always do something like this:

A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com

RE: Truss Heel Blocking

Quote (Kootk)

I would not want to be the first to specify that in my domain.

We do just that...

RE: Truss Heel Blocking

(OP)
Sorry forgot to post the image:



I don't know that this is really any better than my first shear panel but at least it positions the vent holes up high out of the way of the insulation and it gives a solid nailing surface for the sheathing to the vent blocks. It does get us back to using the A35 clips though, so back to messing around with hardware.

A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com

RE: Truss Heel Blocking

The high heel height allows more insulation with ventilation between the roof sheathing and the top of the insulation. Normally just a matter of securing the outside wall sheeting to the higher heel and carrying it down the wall to anchor it. A higher heel also permits a greater anchorage of the roof truss system.

Dik

RE: Truss Heel Blocking

Quote (jdengineer)

We do just that...

Beautiful. You're living my dream man! Got one for when the walls terminate at a location where it's not an exterior corner? When I imagine it in my head, it's hard to get the edge of the nearest truss heel panel thing to line up with your boundary studs below.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Truss Heel Blocking

(OP)
Looking at it now I see that one could probably nail up through the shear panel top plate into the vent block with about four 16d nails and probably not have to use the A35 clips, not sure why I didn't see this before. Looking at it in 3D helps sometimes.

A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com

RE: Truss Heel Blocking

medeek,

Your illustrations are really cool!

You should write a book. It could be called, "Blocking Between Truss Heels and Other Things Contractors Don't Want to Do."wink

DaveAtkins

RE: Truss Heel Blocking

That blocking requirement isn't isolated to just NC. The same prescriptive wall bracing provisions are in the IRC2009 R602.10.6.2 for heel depths greater than 9 1/4".

RE: Truss Heel Blocking

(OP)
I use SketchUp for conceptual stuff, I used to draw a lot of hand sketches but I find SketchUp is much quicker for many things. All of my 2D drawings are in AutoCAD but I prefer 3D when I'm trying to visualize a specific construct, it helps things pop out that you sometimes miss with a 2D sketch or drawing. I've managed to cobble together a couple of extensions for SketchUp which allows me to quickly generate roof, floor and foundation geometry (I use a third party plugin for wall framing), so in almost less than a minute I can usually create a fairly realistic model of just about any residential framing or structural issue. I've used a lot of 3D softwares (AutoCAD, SolidWorks, Catia, Chief Architect, etc...) and I can safely say that SketchUp beats them all hands down when it comes to speed and simplicity.

A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com

RE: Truss Heel Blocking

(OP)

Quote (dik)

The high heel height allows more insulation with ventilation between the roof sheathing and the top of the insulation. Normally just a matter of securing the outside wall sheeting to the higher heel and carrying it down the wall to anchor it. A higher heel also permits a greater anchorage of the roof truss system.

If the wall sheathing extends up over the raised heel without a break then yes this is a major advantage to the roof construction as far as uplift and even truss overturning, the question is do most contractors do this or do they just break the sheathing at the top plate and then patch on more sheathing at the raised heel?

That is why I like my 2nd option with the heel block on top of the shear panel. This allows the contractor to terminate the sheathing at the underside of the top chord of the truss, the sheathing is continuous up the entire wall and over the raised heel. The heel block then provides an uninterrupted load path to the roof diaphragm. I don't see the validity in those shear panels with an air gap between their top plate and the roof sheathing, load cannot be transferred through thin air.

A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com

RE: Truss Heel Blocking

Quote (medeek)

do they just break the sheathing at the top plate and then patch on more sheathing at the raised heel?

since walls are generally 8'-1 1/8" or 9'-1 1/8" this is less of an issue than you think. They start the sheathing at the sill plate on the foundation wall, span it over the floor system, and then up the wall. It usually means the 8' mark from the bottom of the sheathing ends up being a foot or two below the top plates. The good home builders alternate whether the infill piece is at the top or bottom.

RE: Truss Heel Blocking

(OP)
The problem with my first shear panel option shown is that the contractor would have to notch around the top chords of the truss, too much hassle and then you are still left with having to punch holes in the sheathing for the ventilation and its hard to control how big these holes may be so the shear panels are probably compromised.

The downside of Option #2 is that you have both shear panels and heel blocks to install, but I don't supposed you would need the shear panels every truss bay, just over the identified shear walls and maybe every other bay where no shear walls are present, I guess it really depends on how conservative you want to be.

A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com

RE: Truss Heel Blocking

Manufactured truss blocking is about the easiest and least expensive thing you can specify for anything over a 10-12" heel. Specify it with a bevel at the top so you get good edge nailing. For shear walls, you can give the truss manufacturer the lateral load each block needs to be designed for (keep it simple). They will build the block to resist the load. You do however need to resolve over-turning forces on the block. Usually you can get away with toe-bailing the block to the trusses, sometimes you need A34's or A35's.

I will Post a detail later.

IF you aren't supplying blocking, how are you justifying your load transfer.

RE: Truss Heel Blocking

Quote (cbse)

IF you aren't supplying blocking, how are you justifying your load transfer.

Hopes and prayers mostly

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources