Max Demand Calculation for a Feeder
If One utility company have details of Consumption (KWH) per Distribution Transformers (11/0.433KV) per month. How to calculate the Max Demand on that 11KV feeder, using this Consumption KWH information? Is there any formula suggested by IEEE Standards for the same, Please advise,
RE: Max Demand Calculation for a Feeder
The demand will be based on KVA rather than kW.
There may not be much correlation between monthly consumption and maximum demand.
If a feeder is under the jurisdiction of the applicable code, the calculated demand will be a code matter.
If the feeder is owned by the utility they will most likely use a chart based on experience and the types of loads serviced by the feeder.
Bill
"Why not the best?"
Jimmy Carter