Brick Tie Attachment to Substrate
I am working on a project where the owner and contractor want to put a brick veneer on an existing metal building. The existing building is clad with 26 gauge reverse applied PBU panels over metal girts. The girt spacing is to large to allow direct attachment of the proposed brick ties to the girts and also satisfy the area/spacing requirements for brick ties. My hesitation is that I cannot provide a pullout capacity for screws attached to 26 gauge panels. I remember in the past, a required tie/attachment capacity of 100#'s per tie, but cannot find it now. I want the contractor to use a heavier gauge vertical hat/furring channel system to attach the brick ties. Any input would be greatly appreciate.
RE: Brick Tie Attachment to Substrate
The hat channel would be my first thought. FWIW, it is recommended by the BIA (i think) that 18ga minimum material be used for brick tie attachment.
would there be a thermal expansion differential between the brick and the metal siding....
And the typical PEMB deflection is L/180...
Quote (OldBldgGuy)
Good point. I believe they are even allowed L/60 for the girts.
Hmm,. not sure how you add brick to a giant noodle.