Is there a reason why grounding transformer are wye-delta? If I had some auxiliary loads that I wanted to power from the secondary, could I make it wye (gnd) - wye (gnd)?

RE: Grounding transformer

No. If you wanted to do that you'd need a wye-delta-wye. Without the delta it won't function as a grounding transformer.

RE: Grounding transformer

Or an interconnected star/star. Quite common where I'm from for supplying substation low voltage auxiliary services from the earthing transformer.
Regards
Marmite

RE: Grounding transformer

What do define as an "interconnected star/star"? I've not run into that term.

RE: Grounding transformer

I think the interconnected star/star is also called a zigzag transformer.

RE: Grounding transformer

A zig-zag may be a special order transformer.
Three distribution transformers rated for line to line voltage may be used for the wye:delta grounding bank.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Grounding transformer

(OP)
A zig-zag was my first design preference, but the customer is arguing to establish the ground by ordering a wye-wye unit transformer (2000kva). I modeled the wye (gnd) - wye (gnd) in SKM and did not get single line to ground current. I tried drawing out the zero sequence diagram to understand why no ground fault current but I must be missing something. Can you explain why there is no ground fault current.

RE: Grounding transformer

You'd have to have a zero sequence "source" on the secondary. The wye-wye will pass zero sequence currents from one side to the other, but won't source zero sequence current. Getting a wye-delta-wye may be easier than it appears. A wye-delta-wye can be built on a three legged core while a two winding wye-wye requires at least four legs. In a prior life, I found that it took a tight spec to get a dry type wye-wye of any size that wasn't actually a wye-delta-wye; that third winding can be less expensive to manufacturer and ship than would be the larger core necessary to get a true wye-wye.

RE: Grounding transformer

(OP)
So why does a wye-delta work? The delta can't pass the zero sequence current, so why does it provide a grounding path?

RE: Grounding transformer

Look at the zero sequence diagrams for the various transformer configurations. The wye side of a delta-wye transformer will provide a complete circuit in a sequence diagram; the delta side won't. The wye-wye, if both wyes are grounded, will connect the zero sequence networks across the transformer but does not, in and of itself, complete the circuit; something else will have to do that.

RE: Grounding transformer

As per IEC (60076-1)and IEEE (C57.12.70&80) the correct term for the proposed connection is zigzag or Z connection. It consists of two halves in series,but the two halves in different phases (or limbs of core) . To get a grounding transformer only Z winding is sufficient. Only in case of auxiliary supply requirements, an additional star winding is required. Compared to a star winding, Z winding requires 1.15 times more copper and a star /delta unit will require double the quantity of copper in star winding. Hence the economy and advantage of Z connection for grounding transformers. During an LG fault,Z connection will allow fault current to flow in three phases together to return through neutral.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources