Time interval for measuring transients in SCADA

Time interval for measuring transients in SCADA

Time interval for measuring transients in SCADA

(OP)
We have a problem with relays tripping at our power plant.
We believe it may be due to transients but need to make accurate measurements to be sure.
Our current SCADA software (Siemens WinCC) measures 16 points at our power plant, every 500 milliseconds.
I asked the SCADA "expert" why we cant speed-up the measuring intervals to 1 wave for example (20 milliseconds at Hz=50).
He said that impossible because:
"There is not any defined time duration. System reads the data sequentially. It reads the first point,
then reads the second point, etc. it returns to the start point after last point read.
It looks, this sequence takes approx. 500 milliseconds and you cannot change it."
Im not sure if this is software limitation (Siemens WinCC) or of our sensors?
But I believe we can't measure and track down transients accurately with a 500 milliseconds measuring interval.
Agreed?
And what can we do about?
Do we need to change the sensors and/or the software?

RE: Time interval for measuring transients in SCADA

Hi,
Are yours relays, IED ( i.e. numerical) ? In this case, the best way forward to get use the relays records ( i.e. COMTRADE) for further analysis. such records samples at ( typical values) 20 to 50 samples /cycle.
the outstanding issue will be whether you will be able to (automatiquely) collect the files from relays to SCADA

RE: Time interval for measuring transients in SCADA

No SCADA system is designed for transient fault measurement. Either you adapt the solution proposed by ZapSib or you need to find an external TFR. Here's a couple readily on the market:
siemens
abb

-SB

RE: Time interval for measuring transients in SCADA

(OP)
ZapSib, what is COMTRADE? I googled it, nothing seems to relate to electricity ??? Comtradesoftware.com seems like an IT system, or maybe I mis-understand ???

RE: Time interval for measuring transients in SCADA

(OP)
Thank you all! You have me pointed in the right direction.
Happy new years 2017
:)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources