Ferroresonance on Switching Secondary Breakers.
Ferroresonance on Switching Secondary Breakers.
(OP)
The Main Power transformer at unloaded condition. As one of the secondary VCB is switched ON, the power transformer and the auxiliary transformer makes loud rumbling noise. this doesn't always happen, sometimes it occurs and sometimes it don't. The rough SLD is attached. What are the solutions to mitigate this?. It has long secondary single core cables aroud 200 meters.






RE: Ferroresonance on Switching Secondary Breakers.
RE: Ferroresonance on Switching Secondary Breakers.
RE: Ferroresonance on Switching Secondary Breakers.
RE: Ferroresonance on Switching Secondary Breakers.
The PT specification is as below, I have never seen such configuration. The PT is made in russia and this type of configuration is used in russia. I'm still waiting for the translation to get done.
RE: Ferroresonance on Switching Secondary Breakers.
RE: Ferroresonance on Switching Secondary Breakers.
measure their inductance you can add an equal amount of capacitance to neutralize it,
or even some small load, exactly like prc said above.
RE: Ferroresonance on Switching Secondary Breakers.
Sorry, I can't understand how adding shunt capacitors would mitigate this problem. As far as loading resistor at the PT secondary, I understand it to be for avoiding ferroresonant at the PT's. Could you please kindly explain more about this.
My understanding for adding resistors at the PT secondary:
1. Due to switching/Voltage transients causes the PT to go into saturation.
2. If the PT's are saturated means it draws a huge magnetizing current. The PT's remain saturated until the magnetizing current decreases.
3. The Inductance of the PT winding changes during the saturation.
4. Now if the value of the varying Inductance of the PT's during saturation matches with the line to ground capacitance of the system, In other words, the capacitive charging currents of the cables cancels the magnetizing current of primary winding of pt. Then Ferroresonant occurs.
5. So to come out of the saturation for the PT's,the exciting current should be reduced drastically, It can be reduced by increasing the load of the PT.
RE: Ferroresonance on Switching Secondary Breakers.
By shunt capacitor, do you mean Harmonic Filters?
RE: Ferroresonance on Switching Secondary Breakers.
It is usually called surge absorber. Simple shunt capacitors.