Power Load Question

Power Load Question

Power Load Question

(OP)
I have a 480V 50A Breaker, with a transformer 480V/120V that's 25kVA, and a power panel pulling 15A.
Can I add another power panel to the transformer pulling 50A if I increase the main breaker to 100A?
If not, then what's my limiting factor the transformer or the breaker?

RE: Power Load Question

What do your calculations show?

RE: Power Load Question

Code requirements are the limiting factor. Check the NEC.
From your description, I strongly suspect that your present installation is not in compliance.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Power Load Question

is this single phase or 3 phase?

RE: Power Load Question

(OP)
3 phase

RE: Power Load Question

Like Davidbeach said, what does your calculations say?

I suspect the max CB allowable for your TX is 50A. i doubt you can increase it to 100A. You might have to increase the TX size, but again, that depends on your calc/studies. If you do, remember you need to make sure your Panel and your cables are rated for the new ampacity of 100A.

RE: Power Load Question

I would say that the breaker is your limiting factor as your secondary side can handle 122 amps.

RE: Power Load Question

Mary -
Let's get a little bit clearer on the system: We got "480/120", "3 phase", "25kVA".

I've never seen a 25kva, 3ph transformer. That is a single phase size. 3ph would be 30kva.

If the system (transformer and panel, not the 480V feeder) is 1ph, then I would expect 480/240/120

If 3ph, then 480/208/120.

Of course you could have 1ph, 480/120. Not very common, but there are some.

So, what is the system?

iceworm

Harmless flakes working together can unleash an avalanche of destruction

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources