inverter duty motors on soft starts
2

inverter duty motors on soft starts

inverter duty motors on soft starts

(OP)
Do inverter duty motors need to be used with soft starts? Thanks

RE: inverter duty motors on soft starts

Negative. Soft starts do not send millions of sharp-edged waveforms into the motor the entire time it's in operation.

Keith Cress
kcress - http://www.flaminsystems.com

RE: inverter duty motors on soft starts

(OP)
Agreed, but they send some at start-up, albeit not as dramatic. Thanks!

RE: inverter duty motors on soft starts

Actually SSs typically use SCRs that merely gate the line voltage to the motors which is not at all like an IGBT switching full peak line voltage stored on a capacitor bank into a motor. So have at it with your ancient open winding motor. LOL

Keith Cress
kcress - http://www.flaminsystems.com

RE: inverter duty motors on soft starts

Keith's right, apples and oranges here. The main risky issue with inverters is the steep rise time of the pulses, typically 0.1 microsecond for 3rd generation IGBTs, newer 4th gen IGBTs are now as fast as 0.01 microsecond, but only a few micro drives are using those yet.

In comparison, SCR turn-on is in the order of 1000 times slower (upward of 100 microseconds), plus they only turn on once per cycle, not 16,000 times per cycle. SCRs are not a problem for the motor...


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington

RE: inverter duty motors on soft starts

Besides the lack of rise time, some inverter duty motors have a torque curve that doesn't work very well with a soft-starter, or any kind of fixed frequency starting method for that matter.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources