Transformer Diff Protection Problem during the TF Energization

Transformer Diff Protection Problem during the TF Energization

Transformer Diff Protection Problem during the TF Energization

(OP)
Hello every one; now a days i am having a big issue related to the transformer differential relay.
Let me tell you the schemes and parameters:
2 generators (each 125MW) connected with the 1 stepup Transformer(350MVA/15kV-400kV); between generator & TF there is 52G and also two Auxiliary Transformer (15kV to 6.6kV). Aux TF is feeding the MV Switchgear & also stepdown TF (6.6kV to 440V) for LV switchgear.
Differential Protection taking the feedback (through CTs) from HV(400kV), tertiary(15kV) and MV (6.6kV) side. 87 also have REF, 50/51N, Thrmal OL, Overfluxing, Voltage & Frequency Protection...
Problem Case:
1-when we energized the transformer (close Line Breaker); suddenly 87 operate (current differential) and trip the Line breaker.
2-By disable the diff protection; transformer energized and then again we enable it, transformer still energized in healthy condition but when we start 6.6kV induction motor (for cranking the turbine), this relay again trip (87) the line breaker.

If we disable the 87 protection and energize the TF and crank the turbine, after synch the generator we enable 87 then it works properly but during the above cases it trip the line breaker.
Can any body please explain why this is happening?
I think the relay settings for the 87 is not correct; if you want relay settings and trip record (disturbance record); i will share.
Any help regarding to the above cases will be highly appreciated

RE: Transformer Diff Protection Problem during the TF Energization

What do the relay event reports show? The event reports should provide all the answers; start with looking at the phase relationships between sets of CTs.

RE: Transformer Diff Protection Problem during the TF Energization

Sounds consistent with incorrect wiring on CT inputs as David is suggesting. With diff protection disabled, look at the CT currents coming into the relay. Depending on the setting of the differential element, it may not see enough "difference" current to trip at low load, even though CTs are not wired correctly.

RE: Transformer Diff Protection Problem during the TF Energization

1. Check the CT compensation
2. Check the restraint elements

RE: Transformer Diff Protection Problem during the TF Energization

Please check the second harmonic content in the inrush current and relay setting for second harmonics. In large GTS of recent make,the second harmonic content during inrush has come down drastically ( below 10 % compared to > 20 % earlier days) This happened due to change in CRGO grades used in modern transformers plus some changes in constructional details. Normally harmonic restraint setting of relay is 10-15 % and if actual harmonic content is <10 % the relay will take it as a fault current and actuate the relay. Some different restraining features are being introduced in modern relays to overcome this situation during inrush current.

RE: Transformer Diff Protection Problem during the TF Energization

(OP)
Thanks All; Kindly reply me your emails, so i can send you the setting and disturbance recorder files.



RE: Transformer Diff Protection Problem during the TF Energization

I suggest you put your settings/DR etc .. on e.g. DROPBOX ( or equivalent) and share here the link.

RE: Transformer Diff Protection Problem during the TF Energization

Thanks for sharing the files. I also replied to you on linkedin, please check.

RE: Transformer Diff Protection Problem during the TF Energization

I'm seeing nothing but noise on channels 2 through 5. Check your CTs for shorts.
Channel 1 looks bad too, with A and B in phase with each other and C 180 degrees out from the other two.
The schematic indicates every CT secondary neutral is grounded twice, one ground through a switch. Unless the switch is open, you may find that stray ground currents have an improper path through a relay coil.

RE: Transformer Diff Protection Problem during the TF Energization

How can I open the disturbance/event data files?

RE: Transformer Diff Protection Problem during the TF Energization

I used the AcSelerator Quickset Event Viewer application, a free download (after registration) at selinc.com. I suspect most any Comtrade viewer will work.

RE: Transformer Diff Protection Problem during the TF Energization

Check the CT polarity & connections on the 6kv input. Trips occur when there is high current due to inrush or heavy load, indicating a CT wiring or setting issue. Since no trip occurs under normal generation output, either the 400kV and 15 kV generator CT's are correct or the generator output current has been less than the pickup.

If this is a typical gas turbine system, the heaviest 6kV load occurs during turbine starting. Maybe during normal operation, the 6 kV current is less than pickup so no tripping. Or it could be a setting issue or the multiple grounds on CT's.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources