MV IEC Breaker Ratings - d.c. component of breaking current

MV IEC Breaker Ratings - d.c. component of breaking current

MV IEC Breaker Ratings - d.c. component of breaking current

(OP)
If the calculated (prospective) d.c. component of symmetrical breaking current is less than 20%, then the breaker's required interrupt rating is defined by only its symmetrical breaking current. See IEC 62271-100
The definition of d.c. component is defined by the ratio d.c. current / ( sqrt(2)*symmetrical breaking current ).
If a breaker with a rated 30% d.c. component is required to interrupt a calculated symmetrical current of 27 kA with a d.c. component of 65% ,what is the breaker required rated symmetrical breaking current ?

The following formula equates the rated and calculated asymmetrical rms current:

Rated Asymmetrical = Calculated (prospective)Asymmetical
Isc ( 1 + 2 %DC^2 ) ^0.5 = Ib sym ( 1 + 2 % d.c.^2 ) ^0.5

Isc ( required rated symmetrical breaking current ) = 33.76 kA Use next highest standard IEC breaker rating of 31.5kA.

Assuming the actual breaker symmetrical breaking current rating was 33.76kA, then the max permissible d.c. component would be 0.30 * sqrt(2) * 33.76 = 14.32 kA.
A HV breaker can not interrupt d.c. current, however if the ratio of d.c. current / sqrt(2)* symmetrical breaking current is maintained, then sufficient current zeros occur to enable the breaker to extinguish the arc.

Can anyone out there in IEC land confirm the following ?
If the calculated (prospective) Ib sym is less than rated Isc, the above formula can not be used to calculate a higher permissible d.c. breaking current because te ratio d.c. current / sqrt(2)* symmetrical breaking current must not be less than the breaker d.c.component ratio.
See attached file for calculations.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources