Lightning protection of a 200 ft long pipe
Lightning protection of a 200 ft long pipe
(OP)
Guys,
I am trying to protect the following pipe against lightning. What is your suggestion?
1- To put air terminals every 50ft along the pipe
2- Using static mast at both ends of the pipe and running a wire along the pipe?
3- Any other suggestion?
I am trying to protect the following pipe against lightning. What is your suggestion?
1- To put air terminals every 50ft along the pipe
2- Using static mast at both ends of the pipe and running a wire along the pipe?
3- Any other suggestion?






RE: Lightning protection of a 200 ft long pipe
7.3.2 Zone of Protection for Masts and Overhead Ground Wires. 7.3.2.6 Overhead Ground Wire.
One row of ground wire and supporting mats it is enough-if the pipe will stay in 30 m protecting radius.
It depends on wire material, wind and ice in order to calculate the maximum span. However 100 ft. in my opinion, it will be o.k.
RE: Lightning protection of a 200 ft long pipe
RE: Lightning protection of a 200 ft long pipe
art.7.1.2.1 “Metallic structures that are electrically continuous; tightly sealed to prevent the escape of liquids, vapors, or gases; and of 4.8mm(3⁄16 in.) thickness or greater to withstand direct strikes in accordance with 7.3.2 shall be considered to be inherently self-protecting.”
However, if there is a flammable material involved, all appurtenances where flammable concentrations of vapor or gas escape to the atmosphere shall be closed or otherwise protected against the entrance of flame.
By-the-way, from art.7.3.2 important is the grounding method and end protection.
RE: Lightning protection of a 200 ft long pipe