Double Bus Bar switch gear
What is double bus bar gear used for? Has anyone ever installed it or seen it in the field? I personally can not understand this concept or why its even being offered.
https://library.e.abb.com/public/22ace6a787018c48c...
http://ms.schneider-electric.be/Main/PIX/catalogue...
RE: Double Bus Bar switch gear
http://electrical-engineering-portal.com/abb-mv-sw...
The supplied costumers sometime cannot be separated in a fault case, if you have
not a redundant busbar. In some instance-in very important installation in which the interruption of energy supply is more expensive than the equipment price as in a large steel complex-even a third busbar, namely a transfer bar, it could be required.
Would you happen to know the behavior of this gear during a bus fault? Would it effect the other bus bar of be contained?
That will very much depend on the protection employed and the type of fault. Bus differential would almost certainly clear the fault before it propagated to the second bar. Plain OC/EF might well allow an arcing fault to persist long enough to compromise both main and reserve bars. If an application is of sufficient criticality to justify the use of a double busbar board then it likely justifies the use of bus differential protection.
Note that repair to a faulted bar would still require the full board to be isolated to undertake repairs, or at least it would under our Safety Rules. The potential benefit of the double busbar is that supply could (possibly) be restored to the load until a convenient time was available to undertake repairs rather than having an unplanned forced outage at a hugely inconvenient time.
In the UK dual busbar systems are very common in our transmission substations. Fifty / sixty years ago they were also common in power plants and the like for critical distribution, but today minimising capital cost has a higher priority than long term operability and maintainability and they are much less commonly seen. Improved switchgear reliability probably plays a part in that too, although I think we may soon be seeing a decrease in long-term reliability as a result of manufacturers designing out every last gram of non-essential material to the point where there is absolutely no margin left for wear & tear, operational degradation, or anything of that sort. Modern equipment seems to have far too many failures for which there is no excuse other than bare-minimum level of design and manufacture.
In terms of decreasing reliability and maximizing capital cost I regret to say that is moving toward the transmission level; 400Kv not sparred. Single bus bar is actually now being contemplated at these voltage levels:
Actual busbar faults are very uncommon, I have only seen a couple first-hand on 11kV metalclad gear and both were phase-earth and limited by the NER to a relatively low current. Messy but repairable. Both were suspected to have been initiated by either contamination or PD on a polymer insulator which eventually resulted in flashover.
Most failures that I come across tend to be in or around the moving parts: disconnectors, circuit breakers, main disconnects on withdrawable gear, shutters, earth switches when they leave a pole closed and indicate open... not all on our site thankfully, but the Energy Networks Association in the UK operates a membership-based database of equipment faults which is available to suitable organisations including most of the distribution utilities and some private network operators.
That is the only place I've seen double bus at low voltage.