motor nameplate question - R1/RX/X1/X2/XM?
motor nameplate question - R1/RX/X1/X2/XM?
(OP)
Please see the inserted image of a small 3-phase motor name plate:

I do not understand what the R1, R2, X1, X2, XM terms mean. It seems like the R1, R2 are the number of ohms I should see if I measure from phase lead to phase lead (while disconnected from power source, of course).
However, why is there only 2 of them if there are 3 phases?
tt
My motor has 9 wire leads sticking out of it. When I measured them all (T1 to 2, 3,...9. T2 to 1, 3,...9 etc) I found that T1-T4, T2-T5, T3-T6 all measured 4.8 ohm each. Any combination of T7,8,9 measured 8.9 ohm.
Outside of those measurements, all other leads to each other were in the megaohms
The measurements between motor leads suggests, per the chart below, that my motor coils are a wye-style load.
But, even if that is true, why I don't I get the 10.8 ohms on the name plate? if there are 3 phases, why is there only R1, R2? What even ARE X1, X2, Xm?

I do not understand what the R1, R2, X1, X2, XM terms mean. It seems like the R1, R2 are the number of ohms I should see if I measure from phase lead to phase lead (while disconnected from power source, of course).
However, why is there only 2 of them if there are 3 phases?
tt
My motor has 9 wire leads sticking out of it. When I measured them all (T1 to 2, 3,...9. T2 to 1, 3,...9 etc) I found that T1-T4, T2-T5, T3-T6 all measured 4.8 ohm each. Any combination of T7,8,9 measured 8.9 ohm.
Outside of those measurements, all other leads to each other were in the megaohms
The measurements between motor leads suggests, per the chart below, that my motor coils are a wye-style load.
But, even if that is true, why I don't I get the 10.8 ohms on the name plate? if there are 3 phases, why is there only R1, R2? What even ARE X1, X2, Xm?





RE: motor nameplate question - R1/RX/X1/X2/XM?
Note that you should make a Ohm-measurements at high voltage connection ( join 4-7; 5-8; 6-9), but I don't know whether or not the internal Wye is accessible. If not, try to measure the ohms between two phases and divide by 2.
http://winding.wixsite.com/design
RE: motor nameplate question - R1/RX/X1/X2/XM?
10.8 Ohms seems reasonable when the motor is at operating temperature.
There is enough of the connection diagram visible in the photo to identify this as a wye connected motor so don't worry about the delta connection diagram. (And certainly don't try to use the delta diagram.)
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: motor nameplate question - R1/RX/X1/X2/XM?
Keith Cress
kcress - http://www.flaminsystems.com
RE: motor nameplate question - R1/RX/X1/X2/XM?
1) the motor is permanently connected to a load and the load cannot be run in a rotating auto-tune routine, but they want better performance than you will get with a "static" non-rotating auto-tune, or
2) they want to "hack" the motor performance in some way that the auto-tune would not allow in order to use it for some special application, knowing the likely effects of that hacking.
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
RE: motor nameplate question - R1/RX/X1/X2/XM?
And yes, now that drives are so intelligent, I feel like younger engineers like myself have become ignorant to how things work because we can get them working without really understanding them. Not sure how I feel about that, but it is what it is. time is billable and its always on to the next project, understanding be damned.
RE: motor nameplate question - R1/RX/X1/X2/XM?