Settlement of 61 meters crane's foundation
Hello guys,
I have settlement problem with my crane's foundation.
Crane's foundation consists of four reinforced CFA piles (D=0,5m; 16m height) and plile cap (slab 5,0m x 5,0m x 1,4m).
Yesterday after overhelming od excavation, we removed sheet piles. After removing sheets which was near to excavation's sheet piles (about 1,6m to pile's cap slab edge), our foundation subsided 0.013m towards sheet pile.
I need to find out reason of this incident.
Ground:
0,00m = pile cap level
from 0,00m to -14,00m: homogeneous, fine sand (Id~from 0,65 to 0,80)
from -14,00m to -15,50m: sandy clay (Il~0,4)
from -15,50m: fine sand (Id>0,90)
Groundwater level: -2,00m
I have some ideas, maybe you'll help me to solve this problem:
1. Soil in excavation was compactioned not enough (green line at attached image - Crane_fund_section.jpg). After sheet plie removing, foundation turned towards after-sheeting ground crack. But is it possible with quite small excavation, making so considerable displacement?
2. Maybe good idea would be keep sheeting in ground near to "crane-area"?
3. Groundwater level during removing sheet piles was at -4,50m in excavation and at -2,00m outside. Is it possible, that groundwater flow from out to excavation rotated my crane's foundation?
4. FEM grid of piles consists of 0,5m parts. Isn't it to loose? Maybe designer had to make smaller grid parts near to piles cap/groundwater level? Can it make considerable analyze differences?
If You have ideas for another causes of this settlement, please feel free to help me solve my problem.
At below links you can look at
http://files.engineering.com/getfile.aspx?folder=4...
http://files.engineering.com/getfile.aspx?folder=b...
http://files.engineering.com/getfile.aspx?folder=2...
Ground:
RE: Settlement of 61 meters crane's foundation
I am pretty sure it is about water.
You have dewatered the excavation while keeping sheet piles. Then, you finish your work and removed the sheet piles.
Water behind the sheet piles are rushed to the excavation site, since sudden drop of water level is really dangereous based on the settlement behavior, your crane settled. It should be over by now. How deep is your excavation? If it is not deeper than 10m, it will not affect the clay under sand. Settlement should be done by now. Calm down.
Also you have 3D finite element analysis for crane... Wow.
The sequence of removal should not have been a progression around the foundation. A sequence that moved alternately from one side to the opposite side of the foundation would have helped to allow a reasonable redistribution of stresses. The speed of removal also should have been considered. Slower is better.
How do you plan to verify the capacity of the piles before putting the crane back in service? It would seem that the crane could become unstable if the piles settle under load.