Where did the section not requiring FDC's on systems < 20 heads go?

Where did the section not requiring FDC's on systems < 20 heads go?

(OP)
It is something in the past of long ago that I remember using; if a system had less than 20 sprinklers a fire department connection was not required.

I got a small 16 head system (2,000 sq ft building).

I can not remember if it was less than 20 or not more than 20 but I do remember seeing it and I even used it about three times over the past 41 years.

But in the 2013 edition I can not for the life of me find it. Where did they put it?

RE: Where did the section not requiring FDC's on systems < 20 heads go?

I have a copy of the '89 edition - and the 20 sprinkler omission criteria is in there.

2-7.1

Exception No. 1: The fire department connection may be omitted for systems having 20 sprinklers or less.

The next oldest I have is the '99 edition, and the 20 sprinkler omission criteria is gone.

So, I would guess it was removed in either the '91, '94 or '96 editions.

RE: Where did the section not requiring FDC's on systems < 20 heads go?

(OP)
If I remember right it was in the 2002 version.

I have that buried around somewhere I'll have to look.

The thing is Georgia made the giant leap from 2002 to 2013 and I'm just not familiar with what was in earlier versions yet, working on it.

RE: Where did the section not requiring FDC's on systems < 20 heads go?

The 20 sprinkler criteria doesn't seem to be there. The omission criteria changed, but only slightly. Now instead of 20 sprinklers, it is single-story buildings not exceeding 2000 sq. ft. (which is pretty close to saying the same thing).

8.17.2.2 (3), in the 2013 edition.

RE: Where did the section not requiring FDC's on systems < 20 heads go?

(OP)
Thanks, I looked and looked for that and couldn't find it. Now I know where to go,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close