Where did the section not requiring FDC's on systems < 20 heads go?
Where did the section not requiring FDC's on systems < 20 heads go?
(OP)
It is something in the past of long ago that I remember using; if a system had less than 20 sprinklers a fire department connection was not required.
I got a small 16 head system (2,000 sq ft building).
I can not remember if it was less than 20 or not more than 20 but I do remember seeing it and I even used it about three times over the past 41 years.
But in the 2013 edition I can not for the life of me find it. Where did they put it?
I got a small 16 head system (2,000 sq ft building).
I can not remember if it was less than 20 or not more than 20 but I do remember seeing it and I even used it about three times over the past 41 years.
But in the 2013 edition I can not for the life of me find it. Where did they put it?





RE: Where did the section not requiring FDC's on systems < 20 heads go?
2-7.1
Exception No. 1: The fire department connection may be omitted for systems having 20 sprinklers or less.
The next oldest I have is the '99 edition, and the 20 sprinkler omission criteria is gone.
So, I would guess it was removed in either the '91, '94 or '96 editions.
RE: Where did the section not requiring FDC's on systems < 20 heads go?
I have that buried around somewhere I'll have to look.
The thing is Georgia made the giant leap from 2002 to 2013 and I'm just not familiar with what was in earlier versions yet, working on it.
RE: Where did the section not requiring FDC's on systems < 20 heads go?
8.17.2.2 (3), in the 2013 edition.