Pressure in Fire Water Distribution Lines Higher than Fire Pump Discharge Pressure

Pressure in Fire Water Distribution Lines Higher than Fire Pump Discharge Pressure

Pressure in Fire Water Distribution Lines Higher than Fire Pump Discharge Pressure

(OP)
Hello,

The facility that I work at has an electric fire pump/jockey pump combination to provide water to our fire lines. The max discharge pressure of the fire pump is 145psi, however the lines downstream of the pump are reading at 175psi (when the pump is at rest). I was wondering if any of you would have any ideas on how this is possible? The pressure reading on the jockey pump controller is 152psi.

Any thoughts would be appreciated.

RE: Pressure in Fire Water Distribution Lines Higher than Fire Pump Discharge Pressure

Pressure guage is wrong?
Soil temperature high compared to inlet water temperature?
Jockey pump located 15m higher than pressure guage?

Is inlet tank to pump(s) at high level compared to minimum level ( i.e. is 145 psi based on low inlet level?~

Just guesses as you haven't exactly given us much to go on here.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Pressure in Fire Water Distribution Lines Higher than Fire Pump Discharge Pressure

Thermal expansion

RE: Pressure in Fire Water Distribution Lines Higher than Fire Pump Discharge Pressure

Seems like it is the difference in elevation where the readings are being observed. Is the jockey pump at higher elevation? The fire mains should be buried so there should not be much temperature effects.

Is there a pump curve for the jockey pump?

RE: Pressure in Fire Water Distribution Lines Higher than Fire Pump Discharge Pressure

Is there a problem or just curiosity?

It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)

RE: Pressure in Fire Water Distribution Lines Higher than Fire Pump Discharge Pressure

Since the purpose of this jockey pump is to presumably maintain an elevated pressure at 152 psi, then the downstream pressure of the pump at 175psi SUGGEST a difference in elevation of 53 ft(=23/.433).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close