Dears, If we have a 3phase synchro

Dears, If we have a 3phase synchro

Dears, If we have a 3phase synchro

(OP)
Dears,
If we have a 3phase synchronous generator, mechanically connected to gas turbine. and both the generator and the turbine are off, and by fault the circuit breaker become closed , is the the generator shaft will rotate??
Note : for normal operation after starting the turbine the generator shaft start to rotate and there is a PMG in the generator ,the o/p of the PMG is connnected to AVR and this AVR supply the the exciter stator and the o/p voltage for the exciter supply the main field for generator.
Thanks

RE: Dears, If we have a 3phase synchro

It depends on the design of the rotor but most will develop sufficient torque to rotate the turbine, particularly if the bearing lift oil is available to reduce the breakaway friction between shaft and bearing. It is improbable that the torque will be sufficient to rotate the shaft anywhere near normal running speed, so it will run at a high slip and damage the rotor if allowed to persist. Most modern protection relays have the ability to detect a closure onto a dead machine.

RE: Dears, If we have a 3phase synchro

(OP)
The rotor is salient pole type , 4pole.

RE: Dears, If we have a 3phase synchro

Howdy Mohamed,
I am quite sure that the motor will start to accelerate once the CB is closed, but only if the motor has to be equipped with a squirrel-cage starting winding. Most synch motors are started this way. I trust that your CB is protected against unintended closure.
GG

The pessimist sees difficulty in every opportunity. The optimist sees the opportunity in every difficulty.
Winston Churchill

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources