Impact test exemption for SS materials
Hi guys,
As UG is general requirements for all material in ASME Section VIII, is it required to address para. UG-20(f) for a vessel which completely made from SS? We have already addressed to UHA-51. But the inspector doesn’t accept that.
RE: Impact test exemption for SS materials
Mike
The inspector may be correct.
What’s your idea?
(f) Impact testing per UG-84 is not mandatory for pressure
vessel materials that satisfy all of the following:
(1) The material shall be limited to P‐No. 1, Gr. No. 1
or 2, and the thickness, as defined in UCS-66(a) [see also
Note (1) in Figure UCS-66.2], shall not exceed that given
in (-a) or (-b) below:
(-a) 1/2 in. (13 mm) for materials listed in Curve A
of Figure UCS-66;
(-b) 1 in. (25 mm) for materials listed in Curve B,
C, or D of Figure UCS-66.
(2) The completed vessel shall be hydrostatically
tested per UG-99(b) or UG-99(c) or 27-4. Alternatively,
the completed vessel may be pneumatically tested in accordance
with 35-6.
(3) Design temperature is no warmer than 650°F
(345°C) nor colder than −20°F (−29°C). Occasional operating
temperatures colder than −20°F (−29°C) are acceptable
when due to lower seasonal atmospheric
temperature.
(4) The thermal or mechanical shock loadings are not
a controlling design requirement. (See UG-22.)
(5) Cyclical loading is not a controlling design requirement.
(See UG-22.)
So, all of the items above 1-5 must be met for the exemption. Since there is no mention of UHA steels, you go to UG-84 and follow from there.
Thanks.
so do you agree with the inspector about addressing to UG?