Misplaced Anchor Bolts - Precast Garage

Misplaced Anchor Bolts - Precast Garage

Misplaced Anchor Bolts - Precast Garage

(OP)
The contractor misplaced an anchor bolt group for a precast garage and asked me for a repair. I designed the foundation and the precast engineer designed the precast. Please see attached file for column to foundation detail.

My first idea is to cut the existing bolts at the top of the footing and epoxy threaded rods 18"... The column supports an axial compression load and my understanding is that I need to design the anchors to support 0.02 of the load as a shear load, is that correct?

Any suggestions or repair ideas will be very much appreciated.

RE: Misplaced Anchor Bolts - Precast Garage

I think that was the wrong PDF you wanted to upload.

Professional Engineer (ME, NH, MA) Structural Engineer (IL)
American Concrete Industries
www.americanconcrete.com

RE: Misplaced Anchor Bolts - Precast Garage

(OP)
During my research I have discovered Section 3.3.1 in the PCI manual that requires 200 x Area of the column for tension. For my project that equals 200 x 24" x 24" / (4 bolts) = 28,800# of tension per bolt

RE: Misplaced Anchor Bolts - Precast Garage

You appear to have a 2" space. Could you use a plate tapped with threads? I suspect you will need some stiffeners, but I would bet that will still be cost effective.

RE: Misplaced Anchor Bolts - Precast Garage

NFExp,

Two questions:

1. Any resolution to this?

2. [And this is me being nosy so feel free to tell me "none of my business"] On the drawing you posted in error I see a W8x58 and a W16x50. Those seem like unusual sizes (especially the W8x58) so I'm curious if they were chosen to maintain clearance or for some other reason such as, perhaps, for combined flexure and compression as might be the case with a drag strut or some other lateral member. Just being curious (and nosy).

Thanks.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources