Lap Splice Tolerance for Masonry
Lap Splice Tolerance for Masonry
(OP)
Anyone know what the tolerance is for lap splice lengths in masonry? ACI 530.1 doesn't appear to list it. It's -1" for all but #14s and #18s in ACI 117, but that's specifically tolerances for concrete construction. ACI 530.1 will kick you to ACI 117 for fabrication tolerances for bar bend diameters, hook tails, etc. but don't know that that covers splice lengths as well.






RE: Lap Splice Tolerance for Masonry
ACI 117 suggests a 2" tolerance for "ends of bars" which is the only thing that I see that might overlap with a splice tolerance.
However, ACI 318 deals with f'c >= 2,500 psi so technically 2,000 psi grout may not exactly correspond.
Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies
RE: Lap Splice Tolerance for Masonry
I can't possibly be the first person to ask this question. Any of the international guys have anything in your codes?
RE: Lap Splice Tolerance for Masonry
RE: Lap Splice Tolerance for Masonry
We do that too - usually round up a bit on the lap length just to be sure.