(OP)
When you print Arc Flash Labels it's typically in the Normal/Utility configuration?
In my project I also have Standby Generator as well. I don't think they would want
two Arc Flash labels.

Ronne

RE: Arc Flash Labels

If you use only one label, it should be for the configuration that gives the highest incident energy.

RE: Arc Flash Labels

Usually, you need to develop two scenarios, one for Utility and the other one for Generator.

Then find the worst case to print on label.

RE: Arc Flash Labels

X2 on the worst case incident energy goes on the label. This is common as if there are ATS and autostart on the gensets, you don't want someone working in lesser PPE. Typically the gensets will result in higher IE than the utility source.
Now if the genset is locked out, then lower PPE than indicated on label could be used. This would all be part of a job hazards analysis and pre-job briefing.

RE: Arc Flash Labels

(OP)
Thanks. If the generator is needed the client has to manual switch it on.
Also the Generator is normally locked out. I will investigate which case
gives me the highest IE.

RE: Arc Flash Labels

RRoc...I hope I wasn't confusing in my reply. The labels should worst case, which usually is the gensets, and the report should contain a table showing what the values are with the utility as a source. Then this table used for job planning. For example if the genset has a value of 23 cal/cm2 and the utility has a value of 9 cal/cm2 it would be more comfortable to work in the 9 cal PPE

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources