Fire damper, Fire wall
Fire damper, Fire wall
(OP)
Hello guys....I have two questions....
1. Can fire dampers be placed on Fire rated bulk head openings?
2. Which code specify which all shaft or duct needs to be fire rated/ fire wall or it is upto the designers choice?
1. Can fire dampers be placed on Fire rated bulk head openings?
2. Which code specify which all shaft or duct needs to be fire rated/ fire wall or it is upto the designers choice?





RE: Fire damper, Fire wall
RE: Fire damper, Fire wall
Your statement about bulk head openings, to what situation are you referring as there are different types of bulkhead?
RE: Fire damper, Fire wall
whoever did the life safety plan should tell you what exactly each wall is.
I know is pedantic, but the term firewall gets misused all the time.
RE: Fire damper, Fire wall
Yes definitely , i was talking about fire rated wall
Well some details about type is mentioned in NFPA 90A...well its the mixture of NFPA and local AHJ...i will give a dig
RE: Fire damper, Fire wall
RE: Fire damper, Fire wall