Hilti Kwik-Con
Hilti Kwik-Con
(OP)
I want to use some Hilti Kwik-Cons for a tension load in a 4" total thickness composite interior slab ( 1 1/2" deck). Hilti's catalog gives ASD pull-out values for 1 3/4" embedment but does not specify a minimum concrete thickness. I also find that their is no ESR report for this product. Just want to make sure I can use these fasteners and not have someone question it later.
Thanks
Thanks






RE: Hilti Kwik-Con
A screw in concrete is somewhere between an undercut anchor and an adhesive anchor. There's a shallow cone failure then a shear failure. Hilit's web site indicates there is a testing report for Miami/Dade County.
RE: Hilti Kwik-Con
RE: Hilti Kwik-Con
RE: Hilti Kwik-Con
1. Contact Hilti for guidance
2. Use the Miami/Dade values
3. Use a different product
RE: Hilti Kwik-Con
RE: Hilti Kwik-Con