ceiling live load

ceiling live load

(OP)
I'm checking a bowstring truss with a ceiling framed into the lower chord. What live load at ceiling would you use and would you apply it simultaneously with roof live load? It looks uninhabitable and I see no signs of storage use.

RE: ceiling live load

If a rectangle 3'-6" X 2'-0" fits between any of the members, a 20 PSF Live Load needs to be applied in that area. Attic live loads are concurrent with roof live load. Use the ASCE 7 load combinations.

RE: ceiling live load

What if the trusses are on 2'-0" centers?

RE: ceiling live load

According to ASCE 7 attic live loads are not concurrent with roof live loads....see Table 4-1, footnotes l and m

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: ceiling live load

If it's a bowstring truss I'm assuming it's a non-residential usage and I believe you would fall under "Storage areas above ceilings" 20 psf live load. This section is not clear if it needs to be combined with roof live load, so I would combine it similar to as noted under footnote "m" referenced by JAE. I would probably be tempted to follow the definition of storage per footnote "l" and only use 10 PSF non-concurrent if you didn't meet the size requirements. Given it is likely non-residential I don't think the code is completely clear, as it is for residential usage.

Depending on the usage, you may also need to review "Primary roof members exposed to a work floor". You may need to design for 2,000# panel point load depending on the space below.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close