canopy and walk ways

canopy and walk ways

(OP)
Per the canopy section and one below,

Even the roofing material has to be non combustible???


8.14.7.3 Sprinklers shall be permitted to be omitted from

exterior exit corridors when the exterior walls of the corridor

are at least 50 percent open and when the corridor is entirely

of noncombustible construction.

RE: canopy and walk ways

The way I read it the answer would be yes, the roofing has to be non-combustible. Matter of fact this is pretty clear to me.

RE: canopy and walk ways

(OP)
Sorry

Meant to say non combustible construction with say metal decking,but combustible roofing material on top of the metal decking??

RE: canopy and walk ways

(OP)
So with the question

Metal decking,

But combustible material on top of the metal
Decking,,,

Still sprinkle the underneath ???

And even if the sides were open, no storage walk way

RE: canopy and walk ways

The word "entirely" tells me sprinkler protection is required.

RE: canopy and walk ways

Concur.

Not much wiggle room on this...

R/
Matt

RE: canopy and walk ways

As a spin to this, what about roof facades that are above the roof framing and sheeting. Are these considered part of the building to be protected.

I have a pre-school that has a tall facade that is about 3'-6' wide and above the roof sheating. I would say that these are more separated than a typical dormer type structure.

Travis Mack
MFP Design, LLC
www.mfpdesign.com
"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/9221...

RE: canopy and walk ways

I believe you are out of the corridor and into something else.

Are they shown on the structural plan? I am assuming the pretty archtictural feature burns.

So, is the ROOF material Non?

R/
Matt

RE: canopy and walk ways

A facade does not equal a canopy in my mind. Like MJ Willis said, it's a building beautification feature.

RE: canopy and walk ways

'...and when the corridor is entirely of noncombustible construction.' The corridor is not a canopy, therefore, the canopy mentioned in the OP should not apply.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close