load flow and motor starting studies

load flow and motor starting studies

load flow and motor starting studies

(OP)
Guys,
I used to study load flow with normal voltage level for utility and define several scenarios in distribution level such as loosing an MCC etc.
I was looking at another study that has only 3 scenarios with 95%, 100% and 105% voltage levels for utility and nothing in distribution level!
Are we really responsible for this much fluctuation in utility voltage? I thought we consider only 2% fluctuation (and relays should trip for more than 2%) and we are responsible for other scenarios that can happen in distribution level.
Do you know any IEEE or PIP standard that clarifies this?

RE: load flow and motor starting studies

ANSI C84.1 is probably your best bet.

It defines the more popular voltage levels for transmission, distribution and services.

Typically, you can expect a +/-5% maximum variation from nominal voltages.

RE: load flow and motor starting studies

(OP)
Thanks a lot, it helped a lot!

RE: load flow and motor starting studies

I hope you are not serious about tripping for a 2% voltage fluctuation. On a daily basis the transmission system swings more than that. Just closing in a single section of transmission capacitors can change the voltage by 2% to 3%. In the western USA, https://www.wecc.biz/Reliability/TPL-001-WECC-CRT-... provides default transmission voltages from 90% to 110% for some contingencies. Voltage deviation is limited to 8% for single contingencies such as a transformer or a transmission line. Allowable voltage deviation is not specified for larger contingencies like bus faults. Utilities are also allowed to adopt less strict criteria than these.

RE: load flow and motor starting studies

To trip on a voltage fluctuation of 2% would make the system less reliable. For LV/MV networks, some people go with a range of +/- 10%.

RE: load flow and motor starting studies

Although the voltage levels specified in the ANSI standard appear to be clear, C84.1 doesn't specify the time period for the measurement. One interpretation might be the 3 phase average voltage over a 1 hour period. Anther interpretation might be the lowest phase voltage for a single cycle. Utility distributions LTCs/voltage regulators usually have time delay of at least 30 seconds before adjusting voltage in order to avoid responding to transient voltages.

You should only trip protective relays in order to protect equipment from harm, not just because of a number in a standard. You might want to take a look at the ITIC curve. Tripping on anything inside the curve may expose your customers to unnecessary outages.
http://www.powerqualityworld.com/2011/04/itic-powe...

RE: load flow and motor starting studies

(OP)
Bacon4life,
Thanks for information on ITIC curve.
What about load flow studies?
My ETAP shows reasonable results when I have 97.5% in utility (voltage in all feeders are greater than 90%).
I would be bellow 90% in many gears if I use 95% in the utility!

RE: load flow and motor starting studies

For load flow study, in my opinion, IEEE Std 399-1997 ch.6.4 Load flow solution methods it could be recommended. Also motor starting study is here: Chapter 9 Motor-starting studies.
IEEE Std 399-1997 IEEE Recommended Practice for Industrial and Commercial Power Systems Analysis

RE: load flow and motor starting studies

(OP)
Thanks Zanoter4,
I looked at Brown and Red books and they exactly talk about standard voltage ranges etc for different studies!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources