Fire Hydrants and Building Sprinkler Lines

Fire Hydrants and Building Sprinkler Lines

(OP)
I have a small site with a single story building(7,000 sf) that will have a fire sprinkler system. It will be supplied by a 6-inch fire line off the public 8-inch main about 150-ft distant.

The local water authority is saying I may also connect a private fire hydrant off this 6-inch fire line. It will be the hydrant closest to the FDC connection on the building.

Seems problematic to me to have the fire line which supplies the building sprinklers, to also supply to the nearest fire hydrant (which in an emergency, would be used to charge the FDC connection).

I haven't found anything specifically prohibiting this, anyone have an opinion on that?



RE: Fire Hydrants and Building Sprinkler Lines

This is typically done so that the fire department can pump from the fire hydrant into the sprinkler system through the FDC. This provides higher flow to the sprinkler system than you would get with just system pressure.

HTH

RE: Fire Hydrants and Building Sprinkler Lines

I would also be concerned that this is a private fire hydrant. You normally want the District to maintain/flush these hydrants and not the building owner.

RE: Fire Hydrants and Building Sprinkler Lines

You should first do an evaluation of the water supply to the sprinkler by taking into account one or two hose stream deduction, depending on the requirement, from the proposed fire hydrant. One hose stream is equivalent to 250 gpm

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close